Connection lost between APCBE agent and UPS (USB Connection)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Connection lost between APCBE agent and UPS (USB Connection)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:49 AM

0 Likes
3
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:49 AM

Connection lost between APCBE agent and UPS (USB Connection)

Hello,

I have many issues with my APC Smart-UPS SRT 2200VA and the software Powerchute BE connected with a USB cable. After installing the software on a virtualized Windows Server 2016 we receive a lot of mails to inform us that the connections between the UPS and the agent are lost and the connection is established again after many second.

After check the log on the web interface and the eventvwr who confirm the disconnection, I increased the time for a time out in the console agent to 50 seconds. It worked during few days but now we have a big disconnection between the UPS and the server around 5 minutes (see screenshoot) and it's very random. I've already check in the eventvwr if the server enter hibernate mode or somethings like that but no... the only error in the eventvwr for the server it's a WSUS who don't synchronize with the catalog... We have tried to reinstall the software on W2008R2 and change the USB cable without result... I have tried uninstalling and reinstalling the drivers, changing USB ports and rebooting the computer but the problem is still here...

So I do not know what to do... Any ideas ? 

Thank's for your help

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

Hi,

On 12/12/2017 8:31 AM, alexandre said:

Server 2016 is a VM running on a ESXi 6.0 update 1

Not sure how this will react as it has not been tested and not a supported configuration. One Thing that you would need to be sure of is the USB port is dedicated to the Server 2016 VM. That might resolve the comm issue but be aware unless the user writes a script that the PowerChute Agent will run only the Server 2016 VM will be powered down. 

On 12/12/2017 8:31 AM, alexandre said:

AP9631 you think it's better than USB ? and with this card we can use an Appliance ?

 With the AP9631 you can install the PowerChute Network Appliance VM and it would communicate with the host so that all of the VMs and the host are powered down when the UPS switches to battery. PowerChute Business Edition Agent will install on VMware vMA and perform the same duty however at this time only Serial comm is supported. 

In either of the above solution there is no need for the user to write a script since the code is embedded in the PowerChute software. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

Hi,

Sorry for the inconvenience. 

On 12/8/2017 10:24 AM, alexandre said:

I have many issues with my APC Smart-UPS SRT 2200VA

What is the exact model and serial number of the Smart-UPS?

On 12/8/2017 10:24 AM, alexandre said:

After installing the software on a virtualized Windows Server 2016

Is the Server 2016 a VM running on a host or is the system the host? If it is a VM running on the host what is the host OS?

Is there a serial port available? If not would you try using a USB to Serial converter or consider purchasing a serial port card for the system?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

Hello Thank's for your answer The exact model is Apc model srt2200 xli http://www.apc.com/shop/mk/en/products/APC-Smart-UPS-SRT-2200VA-230V/P-SRT2200XLI for the serial number I asked my customer, I will have the answer soon The Server 2016 is a VM running on a ESXi 6.0 update 1 Yes there is a Serial port according to my client, I ask to my him if he want try with a Serial to USB but we need to order one.. And if we buy this card http://www.apc.com/shop/mk/en/products/UPS-Network-Management-Card-2-with-Environmental-Monitoring/P... you think it's better than USB ? and with this card we can use an Appliance ? Thank's for your help (Sorry for the layout, I don't know why there is no space between my sentences...)
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

Hi,

On 12/12/2017 8:31 AM, alexandre said:

Server 2016 is a VM running on a ESXi 6.0 update 1

Not sure how this will react as it has not been tested and not a supported configuration. One Thing that you would need to be sure of is the USB port is dedicated to the Server 2016 VM. That might resolve the comm issue but be aware unless the user writes a script that the PowerChute Agent will run only the Server 2016 VM will be powered down. 

On 12/12/2017 8:31 AM, alexandre said:

AP9631 you think it's better than USB ? and with this card we can use an Appliance ?

 With the AP9631 you can install the PowerChute Network Appliance VM and it would communicate with the host so that all of the VMs and the host are powered down when the UPS switches to battery. PowerChute Business Edition Agent will install on VMware vMA and perform the same duty however at this time only Serial comm is supported. 

In either of the above solution there is no need for the user to write a script since the code is embedded in the PowerChute software. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of