Posted: 2021-07-09 01:12 AM
This question was originally posted by Eric on APC forums on 12/4/2019
Hi all,
My question is, can I tell PowerChute or the UPS itself to delay turning on the power outlets on the UPS for a set amount of time once power has been restored?
Basically, I'm looking for a 30 minute delay before powering my servers/switches/miscellaneous hardware back on to give the battery some time to recharge.
I've messed around with both the Power On Delay and Min Return Runtime settings under Configuration>Outlet Groups on the devices, but neither has had the effect I was hoping for.
Seems a simple thing to do, but I'm having a heck of a time getting it to do what I want it to.
Thanks for any guidance...
Eric
Posted: 2021-07-09 01:13 AM
This reply was originally posted by Bill on APC forums on 12/5/2019
Hi,
You can configure outlet on delay using PowerChute Business Edition or through a Network Management Card.
In PCBE the settings are found under outlet sequence.
In the example above outlet group 2 has been configured as the group the PCBE server is plugged into.
If you have a network management card the setting will be found under configuration - outlet groups.
Posted: 2021-07-09 01:12 AM
This reply was originally posted by Bill on APC forums on 12/4/2019
Hello,
What is the model UPS and how may amps are being drawn?
Posted: 2021-07-09 01:12 AM
This reply was originally posted by Eric on APC forums on 12/4/2019
I have 30 different UPSs to configure in this manner from California to Florida. Most (but not all) are Smart-UPS X 3000s
For the sake of this exercise I'll use a Smart-UPS X 3000 in one of my Florida offices. It's current load is 6.6A
Posted: 2021-07-09 01:13 AM
This reply was originally posted by Bill on APC forums on 12/5/2019
Hi,
You can configure outlet on delay using PowerChute Business Edition or through a Network Management Card.
In PCBE the settings are found under outlet sequence.
In the example above outlet group 2 has been configured as the group the PCBE server is plugged into.
If you have a network management card the setting will be found under configuration - outlet groups.