Posted: 2021-06-29 05:56 AM . Last Modified: 2024-03-13 12:16 AM
Hi All,
Please let me know if SRT5000XLI SUPPORT AP9622 BMS CARD.
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:56 AM . Last Modified: 2024-03-13 12:16 AM
To add on, SRT5000XLI I believe comes with a built in Network Management Card. Check the rear of the UPS and look for the Network port.
Over the network, the UPS will support Modbus TCP on this UPS. You can also add an AP9635 NMC for Modbus Serial. Though, the cheaper option for that would be the built in Modbus via RJ-45 serial cable Bill mentioned if you need Modbus serial.
AP9622 is NOT compatible with any model UPS beginning with SRT.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:56 AM . Last Modified: 2024-03-13 12:16 AM
Hi,
The SRT5K supports modbus via the built in serial port (RJ45 to Serial cable). See application notes 176 for assistance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:56 AM . Last Modified: 2024-03-13 12:16 AM
To add on, SRT5000XLI I believe comes with a built in Network Management Card. Check the rear of the UPS and look for the Network port.
Over the network, the UPS will support Modbus TCP on this UPS. You can also add an AP9635 NMC for Modbus Serial. Though, the cheaper option for that would be the built in Modbus via RJ-45 serial cable Bill mentioned if you need Modbus serial.
AP9622 is NOT compatible with any model UPS beginning with SRT.