DLA3000RM2U question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • DLA3000RM2U question
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:44 AM

0 Likes
7
1180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:44 AM

DLA3000RM2U question

Hi,

We have an old DLA3000RM2U which was purchased in 2004, I replaced batteries recently, "Replace battery" light is off now, but "Battery charge" lights flashing simultaneously. Battery condition shows Good, but the runtime shows only 1 minutes remaining ( on windows server control panel). Do I need replace UPS itself or some other thing I can try? Will battery calibration help and how to do this? never did this before.

Thank you in advance for your help.

Allan

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
1180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM


I will keep an eye on it and see what happens during the next power outage.

Thank you so much for your help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:44 AM

0 Likes
0
1180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:44 AM

Here is a good start smile

Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US

Do you have PowerChute or a Network Management Card installed? Option 1 could be checked through one of those tools if you recently changed that setting. If not, it might not be a factor. For option 2, this would be if you recently increased the load which brought down the runtime or it could be that and what option 3 talks about.

How much runtime do you usually get? Since you've replaced the batteries, have you confirmed during an outage it provided more than 1 minute?

The most common cause/solution for this is usually option 3 but please read through and let me know if you have any questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:44 AM

0 Likes
0
1179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:44 AM

Thanks Angela for your reply. I have PoweChute installed.it shows:

Device Status: Battery discharged

UPS Load: 37.0%

Runtime Remaining: 1 Minutes

I don't know how much runtime usualy get as I'm new here and I haven't confirmed if it will provide more than 1 minutes during an outage.

I did a Seif-test and passed. Runtime calibration currently unavailable,  but it was there before I run self-test. How can I calibrate batteries then?

Thx.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
1179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

I logoff and log back,  Runtime Calibration show up now. Since the runtime is only 1 minute, if I do runtime calibrfation, will this cause connected devices down?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
1179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

Hello again

If you issue a calibration through the software, no, the UPS intention is to go on battery and discharge to between 10 and 20% charge and then charge back up.

I would not be surprised since the reported runtime is so low that it aborts a calibration because of the particular predicament and it is not smart enough to realize that because it has virtually no runtime. If it was a little higher like 2-3 minutes, it might have time to re-calculate before aborting (assuming you get the real runtime you should - which I am sure is at least 15-20 minutes minimum).

If it does abort, our next best bet is to do the manual runtime calibration outlined in that article.

For best results no matter how the calibration gets done, make sure to meet the requirement with 30% load, which you do, and then make sure it does not fluctuate as noted in the article too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
1179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

Hi,

I did a Runtime Calibration through PowerChute, after that, Device Status shows On line and Runtime Remaining changed to 9 minutes, but the Runtime Calibration Result shows Unknown, and Runtime Calibration Date shows Value Not Found. Is this OK now?

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
1179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

I can't explain why the fields didn't update but 9 minutes still seems a bit low. I cannot get the runtime for this discontinued unit without jumping through 19 hoops since it is not on the website but my gut and extra checking tells me it ideally should report more like 18-20 minutes.

When you did the calibration, can you tell how long it actually ran on battery for?

Lastly, the runtime reported is an estimate and when the unit goes to battery operation it constantly updates and recalculates this. A runtime calibration should do that but I'd also be curious to find out and understand if it is reporting 9 minutes but lasting more like 18-20 minutes. So, we also might just need to wait for a battery discharge to see if it more accurately reflects the runtime rather than doing a bunch of calibrations and decreasing battery lifetime.

In summary, I am sure its fine and I'd keep an eye on it and during the next power outage, make a note to check the runtime reported and ensure it lasts closer to 18-20 minutes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
1181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM


I will keep an eye on it and see what happens during the next power outage.

Thank you so much for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of