Windows 8.1 Application Log - "lost communication with ups"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Windows 8.1 Application Log - "lost communication with ups"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
4
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

Windows 8.1 Application Log - "lost communication with ups"

Hi,

My PC is connected to the SUA2200i via a USB cable. The UPS (my 2nd SUA2200i unit) was purchased in April 2013.

After upgrading to Windows 8.1 an error appears in the Application log. Checked the cable I installed the latest version of PCBE but the error persists. It occurs randomly. Once during a power failure the UPS shut down the machine without warning, and proceeded to shut itself down. 6 front LEDs were flashing in sequence indicating a software initiated shutdown.

I've tried nearly every thing I know to resolve the communication lost issue. No luck. In the end I uninstalled PCBE and let Windows' native power management do its thing. So far so good. But I need the additional UPS management capabilities of PCBE.

Can someone from APC help me with this random communication issue?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

Bill,

Thanks very much for the reply.

I downloaded and installed APCUPSD but the driver installation failed. Windows 8.1 does not allow unsigned drivers to be installed. So I disabled driver signature enforcement and proceeded to install the APCUPSD driver. It accepts the driver and requests a reboot. Once rebooted the Device Manager shows the UPS with a Yellow Bang. Right clicking on it and choosing Properties displays the following message." The device cannot start (Code 10)  {Operation Failed} The requested operation was unsuccessful.

Strange thing is Windows native power management functions well without any loss of connectivity, or at least the absence of error messages in the Windows Application and System logs seem to indicate proper communication.

The UPS' information is:

Model: SUA2200-I

Firmware revision 654.19.I

Manufacture date: 15 March 2013

Serial number B21311001760

USB Firmware revision- 7.4

I hope this is not a hardware issue.

Regards,

Viv

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

Hi,

My PC is connected to the SUA2200i via a USB cable. The UPS (my 2nd SUA2200i unit) was purchased in April 2013.

After upgrading to Windows 8.1 an error appears in the Application log. Checked the cable I installed the latest version of PCBE but the error persists. It occurs randomly. Once during a power failure the UPS shut down the machine without warning, and proceeded to shut itself down. 6 front LEDs were flashing in sequence indicating a software initiated shutdown.

I've tried nearly every thing I know to resolve the communication lost issue. No luck. In the end I uninstalled PCBE and let Windows' native power management do its thing. So far so good. But I need the additional UPS management capabilities of PCBE.

Can someone from APC help me with this random communication issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

Hi,

Random communications losses are extremely difficult to troubleshoot. A couple of options are, If you have a serial port available on the computer you could configure PowerChute to communicate to the UPS via serial. Another option is to install APCUPSD instead of using PowerChute or the native power options. APCUPSD will give you most of the same functionality as PowerChute witht he SUA2200 and uses a different USB driver so it may not be affected the same way as PowerChute is being affected.

This is a screenshot of APCUPSD running on Windows 8 attached to a Back-UPS

1600_pastedImage_0.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

Oliver,

What software are you using? PowerChute Business Edition, APCUPSD, or Power Options through the control panel? PowerChute need the APC UPS driver. APCUPSD has its own driver and Power Options uses HID UPS Battery. Once you have determined that the proper driver is loaded if communication cannot be established between the OS and the UPS you should brain dead the UPS. Kbase FA156611 discusses how to brain dead a Smart-UPS.

We also have Knowledge base document FA163608 that discusses No Communication with UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
0
1292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:08 AM . Last Modified: ‎2024-03-12 04:43 AM

Bill,

Thanks very much for the reply.

I downloaded and installed APCUPSD but the driver installation failed. Windows 8.1 does not allow unsigned drivers to be installed. So I disabled driver signature enforcement and proceeded to install the APCUPSD driver. It accepts the driver and requests a reboot. Once rebooted the Device Manager shows the UPS with a Yellow Bang. Right clicking on it and choosing Properties displays the following message." The device cannot start (Code 10)  {Operation Failed} The requested operation was unsuccessful.

Strange thing is Windows native power management functions well without any loss of connectivity, or at least the absence of error messages in the Windows Application and System logs seem to indicate proper communication.

The UPS' information is:

Model: SUA2200-I

Firmware revision 654.19.I

Manufacture date: 15 March 2013

Serial number B21311001760

USB Firmware revision- 7.4

I hope this is not a hardware issue.

Regards,

Viv

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore