Creating SSL certificate for smart ups sc 450
I am trying to create a certificate to import into a sc 450 ups. I am using the security wizard and after I go through my CA and create the .cer file when I try to import the signed certificate I get the following message 'Error importing cert, code: -32'. Any ideas what that message means?
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:37 AM . Last Modified: 2024-03-18 01:15 AM
Hi,
The interface is the PowerChute Business Edition Agent and the instruction as to how to change the certificate are in FAQ FA165288.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:37 AM . Last Modified: 2024-03-18 01:15 AM
Hi,
There is some information on this error here: http://www.apc.com/us/en/faqs/FA285378
We are actively working on a problem specific to using Microsoft Certificate Authority also.
But, this APC Security Wizard tool you're using is only for use with APC Network Management Cards. As far as I know, a SC450 Smart-UPS works with PowerChute Business Edition as it does not have a SmartSlot where you can install an APC Network Management Card.
For importing a SSL Certificate for use with PowerChute Business Edition, I think these instructions apply: http://www.apc.com/us/en/faqs/FA165288
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:37 AM . Last Modified: 2024-03-18 01:15 AM
Steve - Can you verify the exact model SC450 you have?
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 06:37 AM . Last Modified: 2024-03-18 01:15 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:37 AM . Last Modified: 2024-03-18 01:15 AM
If I log into the UPS and look at the About page the model is listed as a Smart-UPS SC450 RM. It has firmware version 736.1.D. I know they use a self signed ssl cert and I guess I could use that but when I turn https on I get a mismatch error.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:37 AM . Last Modified: 2024-03-18 01:15 AM
Hi,
The interface is the PowerChute Business Edition Agent and the instruction as to how to change the certificate are in FAQ FA165288.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-20 11:55 AM
Is there a Step by step process now that
Updating over 500+ Certificates on Smart UPS's
Looking for the Process and if there is now to update these Smare UPS's in bulk rather than manually per UPS.
Any help would be greatly appreciated