Posted: 2024-09-22 08:52 PM
Recently, we are planning to connect the APC 5000 VA UPS to an IMS 4000 sensaphone for monitoring. However, supplier needs to know the UPS is it contain dry contact output for connection? May I know does this model contain this output? Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-23 06:13 AM
By default the system does not include a dry contact I/O. You would need the NMC (Network Management Card) as a starter and than purchase the dry contact accessory linked here:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-04 10:55 AM
Hi @Teken, how can these dry contacts be configured using the NMC so they can be closed when a specific alarm occurs?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-04 11:37 AM
Please review the installation manual for the dry contact module:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-04 01:18 PM
Yes, but is there any option that enables you to configure each contact to a specific alarm? Or the installation of the dry contact module is by default set to certain alarm events?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-04 01:36 PM
The user manual I linked tells you both dry contacts can be assigned and programmed to a user defined events.
Than activate in the manner you require.