APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
I am attempting to create new certificates for our NMC2 modules that are signed by our CA, instead of the self signed certs.
While attempting to use the NMCSecurityWizard CLI v1.0.1 to create new p15 certificates I encounter the following error.
{
NMCSecurityWizardCLI --import -o apc1out -s apc1.cer -p apc1
NMC Security Wizard Command Line Utility v1.0.1
(c) Copyright 2018 Schneider Electric. All rights reserved.
-----------------------------------------------------------------------------
Unhandled Exception: cryptlib.CryptException: -3: Bad argument, parameter 3
at NMCSecurityWizardCLI.Program.ImportSignedCSR(String sCertFile, String sKeyFile, String sOutFile)
at NMCSecurityWizardCLI.Program.Main(String[] args)
}
I have confirmed that all the file names that are flagged in the above command are correct. It seems to happen no matter what order I put the flags in. I get the same "Bad argument, parameter 3" .
Has anyone seen this error before? If so, any idea how to correct it?
Thanks,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
Hi Ian,
I've been able to create a certificate with no issue using those exact commands and my lab CA.
Can you try using this slightly older version of security wizard and also disable any real-time or on-access AV or IPS that might be interfering with the wizard. Also confirm that you are using the base64 export from the CA.
https://schneider-electric.box.com/s/b0nbkuzqcc1b8ka0r2sa4xzqljua44vl
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
Hi Chris,
This is generally when the SecWiz program doesn't like on of the files that your trying to pass to it, can you follow the steps in the guide below:
https://schneider-electric.box.com/s/wkhf0nwpl40rhmia33hbfuk2j0r7da09
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
I too am seeing the same error and have followed the PDF guide exactly. I am on a Windows Domain also. My SSL certificate is up for renewal on the 30th. Is there anything else I can try? Or can I get access to the old Wizard (pre CLI)?
R:\Certificates (SSL)\UPS\NMCSecurityWizardCLI>NMCSecurityWizardCLI.exe --import -o upsas -s certnew.cer -p upsa
NMC Security Wizard Command Line Utility v1.0.1
(c) Copyright 2018 Schneider Electric. All rights reserved.
-----------------------------------------------------------------------------
Unhandled Exception: cryptlib.CryptException: -3: Bad argument, parameter 3
at NMCSecurityWizardCLI.Program.ImportSignedCSR(String sCertFile, String sKeyFile, String sOutFile)
at NMCSecurityWizardCLI.Program.Main(String[] args)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
Hi Ian,
You can use the old Security Wizard GUI, however Chrome and Chromium based browsers will still show error messages as the old GUI software doesn't fill in a field that they require.
Could you confirm that you are using an unaltered "Web Server" template with a two year expiry?
Also could you post the exact command used to create the CSR?
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
Hi Gavan.
Somehow I was able to get this to work 2 years ago (even with the legacy software). Anyway, I am using a Web Server certificate with a two year validity period.
Request Handling CSPs:
Subject Name:
Extensions:
NMCSecurityWizardCLI.exe --csr -o upsa -c CA -g MFPN -n upsalpha.corp.mfpn.ca -d upsalpha.corp.mfpn.ca -a 10.10.0.50 -e ian@myemail.com
NMCSecurityWizardCLI.exe --import -o upsas -s certnew.cer -p upsa
Thanks,
Ian
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
Hi Ian,
I've been able to create a certificate with no issue using those exact commands and my lab CA.
Can you try using this slightly older version of security wizard and also disable any real-time or on-access AV or IPS that might be interfering with the wizard. Also confirm that you are using the base64 export from the CA.
https://schneider-electric.box.com/s/b0nbkuzqcc1b8ka0r2sa4xzqljua44vl
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
Gavan,
Using the version 1.0.0 it worked first try! It would seem there is something in the newer version which is causing the issue. Thanks for sorting this out for me, and hopefully this helps others having the issue until a fix comes out for the new version.
Cheers,
Ian
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
Gavan,
it's a great day when you wake up and have a solution to a several month long issue.
The older client works like a charm. Suggest you get apc to host it on their download page again because that new one is terrible.
Thanks for the help!
-Chris
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
Hi Guys,
I have exactly the same problem on a number of different UPS's here. I can only find version 1.0.1 of the software and this does not work at when i submit to a Microsoft PKI infrastructure. Is the 1.0.0 version of the software available anywhere to download ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:25 AM . Last Modified: 2024-03-15 05:40 AM
I'm having trouble uploading the CA cert to the NMC. i have no issues creating the SSL though the wizard and getting though our CA server and uploading it is no problem, but the CA cert that goes under Security > 802.1x > configuration. I'm trying to get the UPS 802.1x compliant. after Upload the CA certificate status remains Unknown.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-10 08:17 AM
I have been struggling to get a certificate on several UPSs since the old GUI wizard stopped working. I am looking at this again as I have just set up a new UPS and want to add an SSL certificate.
I am using NMCSecurityWizardCLI.exe v1.0.1 and following the directions from the readme that came with it.
I do get a new .p15 file (once I realised that it would try and overwrite the original key in the .p15 unless I gave it a different name), however it also errors and the resulting p15 file is not importable to the UPS
NMC Security Wizard Command Line Utility v1.0.1
(c) Copyright 2018 Schneider Electric. All rights reserved.
-----------------------------------------------------------------------------
Unhandled Exception: cryptlib.CryptException: -3: Bad argument, parameter 3
at NMCSecurityWizardCLI.Program.ImportSignedCSR(String sCertFile, String sKeyFile, String sOutFile)
at NMCSecurityWizardCLI.Program.Main(String[] args)
I am using the base 64 download to obtain the .cer file from our local CA
I have read in several places that version 1.0.0 works but am unable to find a place to download it and am mystified as to why the version that does not work is all that is available on the downloads pages. This issue seems to have been around long enough
Can anyone tell me where to get either a working version of the utility or a working set of instructions? The links in this post did not work for me
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-02 03:32 PM . Last Modified: 2023-06-05 01:34 PM
Can this link be reshared I am having the exact same issue trying to import certs by our CA. I am looking for older version of this utility and link is not working anymore
@BillP just tagging so if you can help me with new link for the older version of NMC
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-06 08:43 AM
Please can this version 1.0.0 be re-shared? I'm having the exact same problem trying to run:
.\NMCSecurityWizardCLI.exe --import -o PROPERCERT -s certnew.cer -p MYCSR
NMC Security Wizard Command Line Utility v1.0.1
(c) Copyright 2018 Schneider Electric. All rights reserved.
-----------------------------------------------------------------------------
Unhandled Exception: cryptlib.CryptException: -3: Bad argument, parameter 3
at NMCSecurityWizardCLI.Program.ImportSignedCSR(String sCertFile, String sKeyFile, String sOutFile)
at NMCSecurityWizardCLI.Program.Main(String[] args)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-11 06:58 AM
I am seeing "This shared file or folder link has been removed or is unavailable to you." when clicking on the link you provided. Can you provide a new link to the 1.0.0?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-16 03:06 PM
I started a ticket with support to get 1.0.0. It does not do the -3 bad argument exception error like on 1.0.1, but then the UPS gets stuck on "loading certificate..." after uploading the cert. I'm using Windows CA on Windows 2019 and I read it has to do with the RSA.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-14 03:55 AM
Hi. How do I have access to version 1.0.0 or 1.0.4, which in this case works? I can't find that.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-14 04:00 AM
Can someone share the link for version 1.0.0 or 1.0.4 or another one that works? Than you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-14 11:32 AM
I am having this issue and with no way to install the 1.0.0 are we just supposed to use the http? That is not really an acceptable answer
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-15 06:37 AM
Create a ticket to get 1.0.0.
I am using Windows 2019 as the CA and its hash algorithm is configured with SHA384 and it doesn't work with 1.0.0.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-17 04:54 AM
I did, but no feedback yet. Can you send me a link?
I'll use a LetsEncrypt wildcard cert for all my UPSs.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-17 07:47 AM
CourtKPrin are right I had to create a ticket in order to receive NMCSecurityWizard 1.0.0 and that resolved my issue. I now see the results as:
NMC Security Wizard Command Line Utility v1.0.0
(c) Copyright 2018 Schneider Electric. All rights reserved.
-----------------------------------------------------------------------------
Certificate's Issuer Information:
Common Name: <Whatever info you put for this>
Certificate's Subject Information:
Common Name: <Common Name you selected>
Country: US
Valid From: 11/17/2023 (GMT)
Valid To: 11/16/2024 (GMT)
Certificate's General Information:
Serial Number: <long ##:##:.....>
SHA1 Thumbprint: <long ##:##:.....>
[*] Importing certificate 'cert.p15' has successfully completed.
I have been working with a very nice person named Cholo great person I would highly recommend. He also got me setup on a self signed cert until we worked out the error I was having with NMCSecurityWizard.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-12-13 04:19 AM
Hi everyone,
could someone provide me the version 1.0.0?
I asked support but did not got anything.
Regards,
Mr. InOut
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-12-15 10:32 PM
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-30 02:39 PM
I had zero luck with the wizards from APC, so finally used Digicert Utility and OpenSSL.
I used digicerts utility to create the CSR from my laptop, which means the private key was from the laptop.
Made the cert template on the CA by duplicating the template for "Web Server" and changed the expiration date to 10 years out (because who wants to do this twice). I downloaded the cert from the /certsrv/ page on the MSFT CA as a Base 64 .cer.
I then opened OpenSSL and exported the key as a PKCS8 with this command line:
openssl genpkey -out C:\rsakey.pem -algorithm RSA -pkeyopt rsa_keygen_bits:2048
Finally after a day of struggling with it, it accepted the cert. But now I have to figure out how to get it to use the cert for the web interface. I imagine it has to do with EAPoL/802.1X Access? What do you put as the "Supplicant Identifier"?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-19 12:35 PM
I had posted back in November that, "I am using Windows 2019 as the CA and its hash algorithm is configured with SHA384 and it doesn't work with 1.0.0." I recently recreated our PKI and went to a two tier Windows CA with SHA256. I'm now able to create certs which are accepted by the NMC. This works with AP9631 running 7.1.2 and AP9641 running 2.5.0.6.
I want to add that I was able to create a cert with additional DNS names using an INF file. I was able to append the root and sub chain to the cert before doing the import process. I read that the Web Server default template had to be used, but I confirmed that I was able to make a duplicate and still use it. To get it to show available in certsrv, I created the duplicate, made no changes, saved it, renamed it, changed the compatibility to 2016, and modified the permissions a bit.
Steps:
Create CSR using 1.0.0 utility
NMCSecurityWizardCLI --csr -o <csrfilename> -n <commonname> -c <two-character country> -m <state> -l <city> -g <company> -u <department> -e <supportemail> -i http://<upsfqdn> -d <upshostname>
Create san.inf
[Extensions]
2.5.29.17 = "{text}DNS=<upshostname>&DNS=<upsfqdn>"
Create new CSR
certreq -policy -config "<ca server fqdn>\<ca name>" "<csrfilename>.csr" san.inf "<newfilename>.csr"
Request Certificate
Browse to certsrv, copy and paste contents from <newfilename>.csr, select web server template, submit
Select Base 64 encoded and download cert
Append chain to certificate and save as certnewbundle.cer
Import key into certificate
NMCSecurityWizardCLI --import -o <newcertname> -s certnewbundle.cer -p <keyfile>.p15
Finally, upload <newcertname> to NMC web console
I plan to look at what others have done using alternative tools, because I want the renewal automated since the certs expire yearly.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.