MGE Galaxy 3500 - AP9631 NMC On battery Alarm Not Clearing

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • MGE Galaxy 3500 - AP9631 NMC On battery Alarm Not Clearing
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Tafadzwa
Lt. Commander Tafadzwa
Lt. Commander

Posted: ‎2024-06-18 12:36 AM

0 Likes
4
1630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-18 12:36 AM

MGE Galaxy 3500 - AP9631 NMC On battery Alarm Not Clearing

Hi All,

 

I have an MGE Galaxy 3500 that has an AP9631 NMC. When the UPS goes on Battery, I receive Alerts however when utility power is restored and the UPS goes back Online, the On battery alarm does not clear on the NMC even though on the display everything is normal. I am monitoring this UPS via DCE therefore I will repeatedly receive on battery alerts until I reboot the NMC.

This issue was happening before and I thought its the NMC with a problem therefore I changed the NMC but the problem is still happening.

NMC firmware is v7.1.2. 

UPS  firmware is 956.0608.I

 

Any advise on what could be the actually issue will be much appreciated.

Connecting Devices!
Labels
  • Labels:
  • Datacenter UPS
  • UPS Management Devices & PowerChute Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Teken
Kirk Teken
Kirk

Posted: ‎2024-06-18 05:30 AM

0 Likes
3
1604
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-18 05:30 AM

Please provide the event & data logs from the NMC for review. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Lt. Commander Tafadzwa
Lt. Commander

Posted: ‎2024-06-19 06:17 AM

In response to Teken
0 Likes
2
1568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-19 06:17 AM

Hi @Teken 

 

Please see attached Log Files. I noticed that nothing is recorded under Data Logs even though I have set the Interval and Size appropriately.

 

Regards,

 

Tafadzwa.

Connecting Devices!
Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-06-19 07:38 AM

In response to Tafadzwa
0 Likes
1
1558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-19 07:38 AM

The Data Log is deleted when you make changes to its settings such as Size. What is the current interval set to?? For now define it to a 5 minute interval and go back to see if there is any metrics captured. 

 

The Data Log was deleted on:

 

05/22/2024	11:58:10	System	Data Log cleared.	0x0023: 

 

Is the below active fault still present?!?!

 

06/16/2024 16:13:16 Device UPS: An input voltage or frequency problem prevents switching to bypass mode. 0x020F

 

If we assume the UPS hardware is fully operational and not broken / defective. At a high level the unit will remain on battery (IF) the input voltage, frequency, THD, is NOT within the systems defined operating range. What is the power quality like in this location? Does the building have a backup generator? Are there other APC UPS showing the same condition / behavior nearby??

 

If yes, please upload the Data Logs for those systems even if they do not show the same problem.

 

==============================

==============================

 

Network Management Card AOS v7.1.2
Smart-UPS & Matrix-UPS APP v7.1.2
NMC Serial Number: 5A1150T00475

Model: MGE Galaxy 3500 20 kVA
UPS Serial Number: PS1121330536
Firmware Revision: 956.0608.I

Date		Time		Name	Contact	Location	System IP
06/19/2024	15:11:33	BFN-1ST-FLOOR-CR1-UPS	ACSA Helpdesk	BFN-1ST-FLOOR-CR1		10.244.250.202

Date		Time		User		Event	Code
06/19/2024	15:11:33	apc	FTP File transfer started.	0x000C
06/19/2024	15:11:26	apc	FTP user 'apc' logged in from 196.11.18.12.	0x0016
06/19/2024	12:01:13	System	NTP update successful.	0x004A
06/18/2024	09:37:52	System	Web user 'apc' logged out from 196.11.3.45.	0x001F
06/18/2024	09:34:42	apc	Web user 'apc' logged in from 196.11.3.45.	0x0015
06/18/2024	09:30:01	System	Web user 'apc' logged out from 196.11.3.45.	0x001F
06/18/2024	09:26:58	apc	Web user 'apc' logged in from 196.11.3.45.	0x0015
06/18/2024	09:22:43	Device	UPS: Restored the local network management interface-to-UPS communication.	0x0101
06/18/2024	09:22:22	System	Network service started. IPv6 address FE80::2C0:B7FF:FE92:CEEF assigned by link-local autoconfiguration.	0x0007
06/18/2024	09:22:20	System	Network service started. System IP is 10.244.250.202 from manually configured settings.	0x0007
06/18/2024	09:22:16	System	Network Interface restarted.	0x0002
06/18/2024	09:22:07	apc	Network Interface restarting. Web user request.	0x0009
06/18/2024	09:21:22	apc	Web user 'apc' logged in from 196.11.3.45.	0x0015
06/16/2024	16:13:16	Device	UPS: An input voltage or frequency problem prevents switching to bypass mode.	0x020F
06/16/2024	16:13:16	Device	UPS: On battery power in response to an input power problem.	0x0109
06/16/2024	16:10:03	Device	UPS: No longer on battery power.	0x010A
06/16/2024	13:20:21	Device	UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.	0x0210
06/16/2024	13:19:44	Device	UPS: An input voltage or frequency problem prevents switching to bypass mode.	0x020F
06/16/2024	13:19:44	Device	UPS: On battery power in response to an input power problem.	0x0109
06/12/2024	12:39:38	Device	UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.	0x0210
06/12/2024	12:39:23	Device	UPS: No longer on battery power.	0x010A
06/12/2024	12:39:19	Device	UPS: An input voltage or frequency problem prevents switching to bypass mode.	0x020F
06/12/2024	12:39:19	Device	UPS: On battery power in response to an input power problem.	0x0109
06/12/2024	12:37:49	Device	UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.	0x0210
06/12/2024	12:37:29	Device	UPS: An input voltage or frequency problem prevents switching to bypass mode.	0x020F
06/12/2024	05:26:32	Device	UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.	0x0210
06/12/2024	05:26:15	Device	UPS: No longer on battery power.	0x010A
06/12/2024	05:25:56	Device	UPS: A phase synchronization fault no longer exists.	0x022E
06/12/2024	05:25:56	Device	UPS: On battery power in response to an input power problem.	0x0109
06/11/2024	15:31:19	Device	UPS: No longer on battery power.	0x010A
06/11/2024	15:31:14	Device	UPS: On battery power in response to an input power problem.	0x0109
06/05/2024	12:01:04	System	NTP update successful.	0x004A
06/05/2024	11:00:11	Device	UPS: A phase synchronization fault exists.	0x022D
06/05/2024	11:00:11	Device	UPS: An input voltage or frequency problem prevents switching to bypass mode.	0x020F
06/03/2024	09:47:35	Device	UPS: A phase synchronization fault no longer exists.	0x022E
06/03/2024	09:47:35	Device	UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.	0x0210
06/03/2024	09:47:15	Device	UPS: A phase synchronization fault exists.	0x022D
06/03/2024	09:47:15	Device	UPS: No longer on battery power.	0x010A
06/03/2024	09:46:55	Device	UPS: An input voltage or frequency problem prevents switching to bypass mode.	0x020F
06/03/2024	09:46:55	Device	UPS: On battery power in response to an input power problem.	0x0109
05/31/2024	20:52:07	Device	UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.	0x0210
05/31/2024	20:51:46	Device	UPS: An input voltage or frequency problem prevents switching to bypass mode.	0x020F
05/31/2024	19:56:37	Device	UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.	0x0210
05/31/2024	19:56:16	Device	UPS: An input voltage or frequency problem prevents switching to bypass mode.	0x020F
05/31/2024	10:39:42	Device	UPS: No longer on battery power.	0x010A
05/31/2024	10:39:37	Device	UPS: On battery power in response to an input power problem.	0x0109
05/26/2024	14:26:06	Device	UPS: A phase synchronization fault no longer exists.	0x022E
05/26/2024	14:25:46	Device	UPS: A phase synchronization fault exists.	0x022D
05/26/2024	14:19:45	Device	UPS: A phase synchronization fault no longer exists.	0x022E
05/26/2024	14:19:24	Device	UPS: A phase synchronization fault exists.	0x022D
05/26/2024	14:04:46	Device	UPS: A phase synchronization fault no longer exists.	0x022E
05/26/2024	14:04:24	Device	UPS: A phase synchronization fault exists.	0x022D
05/26/2024	13:49:46	Device	UPS: A phase synchronization fault no longer exists.	0x022E
05/26/2024	13:49:24	Device	UPS: A phase synchronization fault exists.	0x022D
05/22/2024	12:09:30	System	Web user 'apc' logged out from 196.11.2.115.	0x001F
05/22/2024	12:05:11	apc	Web user 'apc' logged in from 196.11.2.115.	0x0015
05/22/2024	12:02:30	Device	UPS: Restored the local network management interface-to-UPS communication.	0x0101
05/22/2024	12:02:29	System	SSL: Certificate generation complete.	0x0036
05/22/2024	12:02:09	System	Network service started. IPv6 address FE80::2C0:B7FF:FE92:CEEF assigned by link-local autoconfiguration.	0x0007
05/22/2024	12:02:08	System	SSL: Certificate generation started.	0x0036
05/22/2024	12:02:07	System	Network service started. System IP is 10.244.250.202 from manually configured settings.	0x0007
05/22/2024	12:02:03	System	Network Interface restarted.	0x0002
05/22/2024	12:01:54	apc	Network Interface restarting. Web user request.	0x0009
05/22/2024	12:00:45	apc	SSL enabled (now using HTTPS).	0x002F
05/22/2024	12:00:22	System	NTP update successful.	0x004A
05/22/2024	11:59:26	apc	Web user 'apc' logged in from 196.11.2.115.	0x0015
05/22/2024	11:58:47	System	NTP update successful.	0x004A
05/22/2024	11:58:47	System	Configuration change. 	0x0033
05/22/2024	11:58:11	Device	UPS: Restored the local network management interface-to-UPS communication.	0x0101
05/22/2024	11:58:10	System	Data Log cleared.	0x0023
05/22/2024	11:57:54	System	Network service started. IPv6 address FE80::2C0:B7FF:FE92:CEEF assigned by link-local autoconfiguration.	0x0007
05/22/2024	11:57:52	System	Network service started. System IP is 10.244.250.202 from manually configured settings.	0x0007
05/22/2024	11:57:43	System	Network Interface coldstarted.	0x0001
05/17/2024	13:44:10	apc	Web user 'apc' logged in from 10.244.250.200.	0x0015
05/17/2024	13:44:01	apc	Web user 'apc' logged out from 10.244.250.200.	0x001F
05/17/2024	13:43:57	apc	User 'apc' edited.	0x005C
05/17/2024	13:43:09	apc	Web user 'apc' logged in from 10.244.250.200.	0x0015
05/17/2024	13:42:23	System	SSH/SCP: Host key generation complete.	0x0037
05/17/2024	13:42:07	Device	UPS: Restored the local network management interface-to-UPS communication.	0x0101
05/17/2024	13:41:52	System	Network service started. IPv6 address FE80::2C0:B7FF:FE92:CEEF assigned by link-local autoconfiguration.	0x0007
05/17/2024	13:41:50	System	SSH/SCP: Host key generation started.	0x0037
05/17/2024	13:41:50	System	Network service started. System IP is 10.244.250.202 from manually configured settings.	0x0007
05/17/2024	13:41:45	System	Network Interface restarted.	0x0002
05/17/2024	13:41:37	apc	Network Interface restarting. Web user request.	0x0009
05/17/2024	13:41:11	apc	Configuration change. SNMP access control 2 address.	0x0033
05/17/2024	13:40:45	apc	Configuration change. SSH server access.	0x0033
05/17/2024	13:40:13	System	Web user 'apc' logged out from 10.244.250.200.	0x001F
05/17/2024	13:40:04	apc	Configuration change. Primary NTP server address.	0x0033
05/17/2024	13:40:04	apc	Configuration change. NTP enable.	0x0033
05/17/2024	13:39:54	apc	Set Time.	0x0021
05/17/2024	02:54:11	apc	Set Date.	0x0021
03/03/2021	02:54:11	apc	Configuration change. 	0x0033
03/02/2021	19:54:10	apc	Configuration change. Override Manual NTP Settings.	0x0033
03/02/2021	19:53:50	apc	Configuration change. System location.	0x0033
03/02/2021	19:53:50	apc	Configuration change. System contact.	0x0033
03/02/2021	19:53:50	apc	Configuration change. Host name.	0x0033
03/02/2021	19:53:50	apc	Configuration change. System name.	0x0033
03/02/2021	19:53:13	apc	Web user 'apc' logged in from 10.244.250.200.	0x0015
03/02/2021	19:51:13	apc	Web user 'apc' logged in from 10.244.250.200.	0x0015
03/02/2021	19:50:55	Device	UPS: Restored the local network management interface-to-UPS communication.	0x0101
03/02/2021	19:50:41	apc	FTP user 'apc' logged out from 10.244.250.200.	0x0020
03/02/2021	19:50:41	apc	FTP user 'apc' logged in from 10.244.250.200.	0x0016
03/02/2021	19:50:40	System	Network service started. IPv6 address FE80::2C0:B7FF:FE92:CEEF assigned by link-local autoconfiguration.	0x0007
03/02/2021	19:50:38	System	Network service started. System IP is 10.244.250.202 from manually configured settings.	0x0007
03/02/2021	19:50:33	System	Network Interface restarted.	0x0002
03/02/2021	19:47:19	apc	FTP user 'apc' logged in from 10.244.250.200.	0x0016
03/02/2021	19:47:18	apc	FTP user 'apc' logged out from 10.244.250.200.	0x0020
03/02/2021	19:46:56	apc	FTP user 'apc' logged in from 10.244.250.200.	0x0016
03/02/2021	19:44:28	apc	Web user 'apc' logged in from 10.244.250.200.	0x0015
03/02/2021	19:44:02	Device	UPS: Restored the local network management interface-to-UPS communication.	0x0101
03/02/2021	19:43:53	System	Network service started. IPv6 address FE80::2C0:B7FF:FE92:CEEF assigned by link-local autoconfiguration.	0x0007
03/02/2021	19:43:51	System	Network service started. System IP is 10.244.250.202 from manually configured settings.	0x0007
03/02/2021	19:43:35	System	Network Interface restarted.	0x0002
03/02/2021	19:43:21	apc	Network Interface restarting. Console user request.	0x0009
03/02/2021	19:43:16	apc	Configuration change. TCP/IP default gateway.	0x0033
03/02/2021	19:42:49	apc	Configuration change. TCP/IP	0x0033
03/02/2021	19:42:23	apc	CLI user 'apc' logged in from serial port.	0x0014
03/02/2021	19:38:08	System	CLI user 'apc' logged out from serial port.	0x001E
03/02/2021	19:34:53	apc	CLI user 'apc' logged in from serial port.	0x0014
03/02/2021	19:12:38	Device	UPS: Restored the local network management interface-to-UPS communication.	0x0101
03/02/2021	19:12:28	System	Network service started. IPv6 address FE80::2C0:B7FF:FE92:CEEF assigned by link-local autoconfiguration.	0x0007
03/02/2021	19:12:26	System	Network service started. System IP is 10.50.250.35 from manually configured settings.	0x0007
03/02/2021	19:12:10	System	Network Interface coldstarted.	0x0001
03/26/2016	04:45:31	Device	UPS: The output power is turned off.The output power is turned off due to a low battery.	0x0114
03/26/2016	01:25:58	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/26/2016	01:25:58	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/26/2016	01:25:55	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/26/2016	01:25:55	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/26/2016	01:25:52	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/26/2016	01:25:52	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	21:25:58	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	21:25:58	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	21:25:55	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	21:25:55	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	21:25:52	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	21:25:52	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	18:48:20	Device	UPS: The battery is now installed.	0x0130
03/25/2016	18:48:01	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	18:47:39	Device	UPS: The battery is now installed.	0x0130
03/25/2016	18:47:00	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	18:28:12	Device	UPS: The battery is now installed.	0x0130
03/25/2016	18:27:52	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	18:22:23	Device	UPS: The battery is now installed.	0x0130
03/25/2016	18:21:43	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	18:21:02	Device	UPS: The battery is now installed.	0x0130
03/25/2016	18:20:42	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	18:20:00	Device	UPS: The battery is now installed.	0x0130
03/25/2016	18:19:40	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	18:19:19	Device	UPS: The battery is now installed.	0x0130
03/25/2016	18:18:59	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	18:10:49	Device	UPS: The battery is now installed.	0x0130
03/25/2016	18:10:29	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	17:38:24	Device	UPS: The battery is now installed.	0x0130
03/25/2016	17:37:41	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	17:26:30	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	17:26:30	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	17:26:27	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	17:26:27	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	17:26:24	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	17:26:24	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	17:18:56	Device	UPS: The battery is now installed.	0x0130
03/25/2016	17:16:12	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	17:15:30	Device	UPS: The battery is now installed.	0x0130
03/25/2016	17:08:42	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	17:08:21	Device	UPS: The battery is now installed.	0x0130
03/25/2016	17:08:02	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	17:07:40	Device	UPS: The battery is now installed.	0x0130
03/25/2016	17:07:19	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	17:05:18	Device	UPS: The battery is now installed.	0x0130
03/25/2016	17:04:57	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	17:03:14	Device	UPS: The battery is now installed.	0x0130
03/25/2016	16:59:29	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	16:57:49	Device	UPS: The battery is now installed.	0x0130
03/25/2016	16:54:43	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	16:54:24	Device	UPS: The battery is now installed.	0x0130
03/25/2016	16:54:02	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	16:53:21	Device	UPS: The battery is now installed.	0x0130
03/25/2016	16:53:00	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	16:52:42	Device	UPS: The battery is now installed.	0x0130
03/25/2016	16:31:32	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	16:30:10	Device	UPS: The battery is now installed.	0x0130
03/25/2016	16:29:30	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	16:28:47	Device	UPS: The battery is now installed.	0x0130
03/25/2016	16:21:18	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	16:20:57	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:53:42	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:53:21	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:49:56	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:49:36	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:44:51	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:44:31	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:43:30	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:42:28	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:41:27	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:40:25	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:39:23	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:39:04	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:38:02	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:37:20	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:37:00	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:36:40	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:33:37	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:31:53	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:27:07	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:26:46	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:26:04	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:24:01	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:20:55	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:19:13	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:16:29	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:15:27	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:14:46	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:12:01	Device	UPS: The battery is now installed.	0x0130
03/25/2016	15:06:54	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	15:04:50	Device	UPS: The battery is now installed.	0x0130
03/25/2016	14:56:58	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	14:55:58	Device	UPS: The battery is now installed.	0x0130
03/25/2016	14:55:37	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	14:55:17	Device	UPS: The battery is now installed.	0x0130
03/25/2016	14:54:57	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	14:54:35	Device	UPS: The battery is now installed.	0x0130
03/25/2016	14:54:16	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	14:53:54	Device	UPS: The battery is now installed.	0x0130
03/25/2016	14:30:01	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	14:29:57	Device	UPS: The output power is now turned on.	0x0113
03/25/2016	14:29:57	Device	UPS: The battery is now installed.	0x0130
03/25/2016	14:29:05	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	14:25:22	Device	UPS: The battery is now installed.	0x0130
03/25/2016	14:23:18	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	14:21:36	Device	UPS: The battery is now installed.	0x0130
03/25/2016	14:19:33	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	14:15:48	Device	UPS: The battery is now installed.	0x0130
03/25/2016	14:14:25	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	14:13:24	Device	UPS: The battery is now installed.	0x0130
03/25/2016	14:13:03	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	14:11:41	Device	UPS: The battery is now installed.	0x0130
03/25/2016	14:11:22	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	14:11:00	Device	UPS: The battery is now installed.	0x0130
03/25/2016	14:09:19	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	14:06:54	Device	UPS: The battery is now installed.	0x0130
03/25/2016	13:38:56	Device	UPS: The battery is not installed properly.	0x012F
03/25/2016	13:38:40	Device	UPS: The output power is turned off.	0x0114
03/25/2016	13:38:39	Device	UPS: Restored the local network management interface-to-UPS communication.	0x0101
03/25/2016	13:38:21	System	Network service started. IPv6 address FE80::2C0:B7FF:FE92:CEEF assigned by link-local autoconfiguration.	0x0007
03/25/2016	13:38:19	System	Network service started. System IP is 10.50.250.35 from manually configured settings.	0x0007
03/25/2016	13:38:03	System	Network Interface coldstarted.	0x0001
03/25/2016	13:37:28	Device	UPS: The output power is turned off.The output power is turned off due to a low battery.	0x0114
03/25/2016	13:26:26	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	13:26:26	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	13:26:23	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	13:26:23	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004
03/25/2016	13:26:20	System	Detected an unauthorized user attempting to access the SNMP interface from 10.80.250.193	0x0004

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Lt. Commander Tafadzwa
Lt. Commander

Posted: ‎2024-06-20 02:56 AM

In response to Teken
0 Likes
0
1535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-20 02:56 AM

Hi @Teken 

 

Thank you for your response.

 

The Log Interval was initially set to 10 minutes but I changed it to 2 minutes when I picked up that there was no Data Logs stored on the NMC.

 

Tafadzwa_0-1718876212462.png

 

However, the Data Log file is still empty. 

 

Tafadzwa_1-1718876387495.png

This NMC was installed onto the UPS on May 22 2024.

 

The fault below has been cleared.

 

06/16/2024 16:13:16 Device UPS: An input voltage or frequency problem prevents switching to bypass mode. 0x020F

 

There is a Generator on Site and usually kicks in under 5 minutes. I have attached Logs from another UPS on the same Site which has never shown such behaviour.

 

Regards,

 

Tafadzwa

 

Connecting Devices!
Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore