AP8830 Stuck on "Network Management Card Restarting..."

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP8830 Stuck on "Network Management Card Restarting..."
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
rbartholemy
Crewman rbartholemy
Crewman

Posted: β€Ž2024-06-12 11:24 AM

0 Likes
7
3073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-06-12 11:24 AM

AP8830 Stuck on "Network Management Card Restarting..."

Howdy,

 

My colleague was setting static IPs on our APC PDUs for management purposes, and one went sideways on him. It got assigned an IP in our DHCP range and the management GUI was unreachable from the browser. Seemed easy enough to reset the management card, so I went on-site and did so. It rebooted the card successfully a few times, but the GUI was still not reachable. After the last reset attempt (using a paperclip in the reset port on the device), it never appeared to successfully reset again. The display on the unit is lit constantly and displays β€œNetwork Management Card Restarting…”. The menu buttons have no functionality.

 

I was able to connect a serial cable and interact with it through an SSH connection. I even was able to change the IP address to our desired static IP, but the reboot commands do nothing and the GUI is still unreachable.

 

It’s pretty much exactly this issue. This post did not receive a community response. https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/Metered-PDU-AP8953-stuck-on-NMC-boot/td-p...

 

Anything I can do?

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Teken
Kirk Teken
Kirk

Posted: β€Ž2024-06-13 02:29 AM

0 Likes
6
3063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-06-13 02:29 AM

Please review this APC FAQ as it relates to upgrading the firmware. Along with the steps to reset the unit to a factory state:

 

https://www.apc.com/us/en/faqs/FA237061/

Reply

Link copied. Please paste this link to share this article on your social media post.

rbartholemy
Crewman rbartholemy
Crewman

Posted: β€Ž2024-06-13 10:31 AM

In response to Teken
0 Likes
5
3016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-06-13 10:31 AM

Thanks for this. My firmware version is beyond the affected and remediated versions. Should I just issue a factory reset command then?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: β€Ž2024-06-14 04:17 AM

In response to rbartholemy
0 Likes
4
3003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-06-14 04:17 AM

Yes, and let us know the results. πŸ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

rbartholemy
Crewman rbartholemy
Crewman

Posted: β€Ž2024-06-18 09:02 AM

In response to Teken
0 Likes
3
2893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-06-18 09:02 AM

Howdy. I was on-site yesterday but got a little caught up on the tasks. I'm assuming I'm starting from loading to BootMonitor mode, but I'd like to clarify that process. My questions in bold:

 

  1. Select a serial port at the local computer and disable any service that uses the port.

 

  1. Connect the 940-0144 serial configuration cable to the selected port and to the RJ-12 serial port at the Rack PDU.

​

  1. Run a terminal program such as HyperTerminal, and configure the selected port for: 57600 bps, 8 data bits, no parity, 1 stop bit, and no flow control. I assume I log into the PDU at this time as well?

 

  1. Press the Reset button on the Rack PDU display (using a paperclip or similar), and then immediately press the Enter key 5-7 times rapidly, or until the BootMonitor prompt displays the following: To confirm: I reset the PDU NMC and then, from my logged in Putty session, press the Enter key rapidly?

Rhodes BootMonitor
BM>
 
Thanks, and sorry for the confusion.
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: β€Ž2024-06-19 03:26 AM

In response to rbartholemy
0 Likes
2
2884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-06-19 03:26 AM

Yes, to both questions you posed keeping in mind the following caveat from the APC FAQ.

 

Note: If this does not work, you may need to try to reboot the PDU's management interface by pressing Reset again to get the timing right. Perhaps start pressing Enter before you press the reset button and continue to while you press the pinhole reset button.

Furthermore, if using HyperTerminal, try configuring the port settings, going to Call->Disconnect menu then to File->Properties press the Configure button on that screen and OK to confirm the correct settings. Press OK on the remaining dialog boxes and try the process again.

Reply

Link copied. Please paste this link to share this article on your social media post.

rbartholemy
Crewman rbartholemy
Crewman

Posted: β€Ž2024-06-19 09:39 AM

In response to Teken
0 Likes
1
2856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-06-19 09:39 AM

Thanks. I was able to log into the BootMonitor and pass a factory_reset command, and it indeed factory reset the device, but the physical display is still stuck on "Network Management Card Restarting". 

 

I can set the IP and run other commands through the serial connection still, and have done so. Instead of the browser being unable to connect to the console, I get the attached now. I haven't reinstalled the firmware yet so I'm supposing that'll help me access the interface, but still have some pause about the display not allowing me to interact with it. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: β€Ž2024-06-20 04:52 AM

In response to rbartholemy
0 Likes
0
2854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-06-20 04:52 AM

Please try and issue the format command to see how the unit behaves. Once the format process has completed. Cold boot the PDU by removing AC Mains and waiting ten seconds than reconnecting AC Mains.

 

Let me know what happens . . . πŸ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore