Cooling the room when the UPS is on but the CRAC is off

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Cooling the room when the UPS is on but the CRAC is off
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:18 PM

0 Likes
3
1512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:18 PM

Cooling the room when the UPS is on but the CRAC is off

Last weekend, I discovered my computer room air conditioner is not on UPS. I guess the engineer said it couldn't be, but it's not on the building generator either! Before I get pages on my blackberry from the Netbotz Central this weekend and race in from 2 hours away in Charlestown to prop open some doors and get fans running. ( I can't shut the data center down )

Does anyone know how long the computer room can run with the doors open and fans running before it gets overheated?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:18 PM

0 Likes
0
1512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:18 PM

Last weekend, I discovered my computer room air conditioner is not on UPS. I guess the engineer said it couldn't be, but it's not on the building generator either! Before I get pages on my blackberry from the Netbotz Central this weekend and race in from 2 hours away in Charlestown to prop open some doors and get fans running. ( I can't shut the data center down )

Does anyone know how long the computer room can run with the doors open and fans running before it gets overheated?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:18 PM

0 Likes
0
1512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:18 PM

I found it and attached it. This is the file you were talking about "Transient Heating" .xls There's also another one I made from an APC white paper "Cooling and Power worksheet" .xls which you might find useful.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:18 PM

0 Likes
0
1512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:18 PM

One of the challenges of cooling, as you point out Mr Tuff, is what to do when the lights go out. Uninterruptible power is easy to do, and keeps the servers humming along when utility let's you down. Unfortunately that also keeps the heat coming. Therefore you really need uninterruptible cooling as well.
You can place CRAC units on the gen set, if you have one, but depending on the length of time it takes to get the back up generators running and the a/c started up again, it could be a few to several minutes. In that time span you can have quite a bit of localized recirculation and over heating. In very high density applications, servers can bake in as little as 15-20 seconds when you have a total loss of cooling. Pretty scary indeed!
I have recently done a design, a retrofit of an existing IT space, where the client's needs dictated the need for uninterruptible cooling. I used some InRow RC units, which are chilled water only and can run off a UPS. They have no compressors, so there are no high in-rush currents, which can force UPSs into bypass. Then I added new pumps for the CW loop that were VFD driven. The VFD gives them a soft start, so that can go on the UPS too. The mains were already 6" so I didn't make them any bigger, but I did upgrade the chilled water storage tanks so they were larger, this is just like adding more batteries to the UPS. So now, when the power goes out for this customer, the UPS keeps the pumps circulating the cold water in the pipes, and thru the RC units in the data center. The RC fans keep moving the air thru the space, and now the client has uninterruptible cooling with a calculable run-time for cooling. How awesome am I??

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:18 PM

0 Likes
0
1513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:18 PM

Last weekend, I discovered my computer room air conditioner is not on UPS. I guess the engineer said it couldn't be, but it's not on the building generator either! Before I get pages on my blackberry from the Netbotz Central this weekend and race in from 2 hours away in Charlestown to prop open some doors and get fans running. ( I can't shut the data center down )

Does anyone know how long the computer room can run with the doors open and fans running before it gets overheated?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of