Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Connections for PowerChute BE

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Connections for PowerChute BE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

0 Likes
3
992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

Connections for PowerChute BE

I am needing to setup graceful shutdown on several servers through the SmartUPS 1500 I have.  Since it doesn't have a NMC, I will have to use PowerChute Business Edition.  Do I need to physically connect each server to the UPS, not just for power, but also through USB or serial for communication?   The 1500 comes with only one port for the USB cable.  I was under the impression that the only server needing the USB connection was the server with my PowerChute "Server install".  From there, that server would send the shutdown command to the other servers being managed.  Is that correct? 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

0 Likes
0
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

I am needing to setup graceful shutdown on several servers through the SmartUPS 1500 I have.  Since it doesn't have a NMC, I will have to use PowerChute Business Edition.  Do I need to physically connect each server to the UPS, not just for power, but also through USB or serial for communication?   The 1500 comes with only one port for the USB cable.  I was under the impression that the only server needing the USB connection was the server with my PowerChute "Server install".  From there, that server would send the shutdown command to the other servers being managed.  Is that correct? 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

0 Likes
0
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

Our model is a SMT1500RM2U.  Sounds like the NMC is the best bet.  We actually have physical as well as virtual servers I would like to include in the shutdown setup.

One more question.  I also have an older UPS, a DLA1500RM2U.  Is it possible to use Network Shutdown to control both UPS boxes and all of the servers?

Thanks for all your help with this.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

0 Likes
0
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

Hi Jared,

Unfortunately, each UPS requires an NMC and each PowerChute client physically connected to the respective UPS will be installed and pointed towards the NMC in that UPS.

The DLA1500RM2U will work the same with an NMC and PowerChute. You can set up PowerChute in a redundant UPS scenario if you're saying these two UPSs support devices with redundant power supplies or just set them up individually for "single UPS scenarios.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

0 Likes
0
992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

I am needing to setup graceful shutdown on several servers through the SmartUPS 1500 I have.  Since it doesn't have a NMC, I will have to use PowerChute Business Edition.  Do I need to physically connect each server to the UPS, not just for power, but also through USB or serial for communication?   The 1500 comes with only one port for the USB cable.  I was under the impression that the only server needing the USB connection was the server with my PowerChute "Server install".  From there, that server would send the shutdown command to the other servers being managed.  Is that correct? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore