Back-UPS Pro 1100VA Serial Communication on Windows 7

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Back-UPS Pro 1100VA Serial Communication on Windows 7
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

0 Likes
12
2441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

Back-UPS Pro 1100VA Serial Communication on Windows 7

I am trying to get an old Back-UPS Pro 1100VA (BP1100) to communicate through the serial port to a Windows 7 box. I'm using a 940-0024C cable. I tried PowerChute Personal V3.0.2 but it says it can't find the UPS.

Any suggestions?

Thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-07-01 04:27 AM . Last Modified: β€Ž2024-03-05 02:17 AM

0 Likes
0
2441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:27 AM . Last Modified: β€Ž2024-03-05 02:17 AM

Thanks for the tips, yesterday I repair my old UPS "APC Back-UPS PRO 650", I changed all the capacitors, its 6 TO-220 Transistors, the adjust voltage IC, and the 4 relays, this UPS uses the cable 940-0095B, well I have installed Windows 8.1 Pro on my HP Compaq nx7400 old laptop with its docking with serial port, the Apcupsd daemon, my monitor AOC LM929 19 inches and works great together, I'm so happy because I can access to the UPS readings and now I have an autonomy for 65 minutes for my laptop and my monitor with this UPS. Thank you very much for the settings. πŸ™‚

See Answer In Context

  • Tags:
  • 650
  • apc
  • back-ups
  • pro
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Anonymous user
Not applicable

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

0 Likes
0
2440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

I am not able to install the PowerChute Plus software; I keep getting Windows error "The version of this file is not compatible with the version of Windows you're running." I'm running Windows 7 Pro 64-bit. Tried all possible compatibility settings for the install file but all are a no-go. I've also tried a Serial-to-USB converter attached to the 940-0024C cable with PowerChute Personal but still no communication between my PC and the Back-UPS Pro.

I'll try the HID way without PowerChute Plus next.

Do I have any other options?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

0 Likes
0
2440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

I don't think so unfortunately beyond what you mentioned with Windows 7 Native Support with the serial to USB adapter. I'll defer to Bill P. to make sure I didn't miss anything.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

0 Likes
0
2441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

Try APCUPSD www.apcupsd.com. I will run on Windows 7 and is compatible with the Back-UPS Pro 1100.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

0 Likes
0
2441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

In my search for a solution I had already downloaded and installed APCUPSD. Am now reading the docs.We'll see how this goes.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

0 Likes
0
2441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

Hi,

I forgot to mention, your UPS is simple signaling so you should use cable part number 940-0020 and when installing and configuring the software select simple signaling. Simple signaling is the recognition of whether certain pins of the serial port are high or low, and allows for 3 states only; on battery, low battery and UPS turnoff. I talked with a few people about using the USB converter with simple signaling. The consensus is it should work but none of us have attempted this type of configuration so we are not sure.


Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

0 Likes
0
2441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:18 AM

Hi,

I am using a 940-0024C cable since I had one and according to the APC website both the 940-0020 and 940-0024 cables are recommended for the Back-UPS Pro 1100VA (BP1100).

APC BACK-UPS PRO 1100VA 120V Options - Services, Related Products and More | APC

Options

So that information is not correct? Guess I'll make a 940-0020 and see what happens.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:17 AM

0 Likes
0
2440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:26 AM . Last Modified: β€Ž2024-03-05 02:17 AM

I do believe both with all work. We have only used the 940-0024 with a serial to USB adapter though in our testing on some products in tech support. (Bill and I discussed in person.)

Any luck with apcupsd?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 04:27 AM . Last Modified: β€Ž2024-03-05 02:17 AM

0 Likes
0
2441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:27 AM . Last Modified: β€Ž2024-03-05 02:17 AM

I've decided to build both a "Smart-Custom" and a "Simple-Custom" cable per the apcupsd archive and see what happens. Just need to find the correct value resistor from my parts bin for the "Simple-Custom" cable.

Haven't tried apcupsd with the 940-0024 direct to serial or with the 940-0024 + serial to USB adapter yet, guess I should do that first.

I'll report back what results I end up with.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 04:27 AM . Last Modified: β€Ž2024-03-05 02:17 AM

0 Likes
0
2440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:27 AM . Last Modified: β€Ž2024-03-05 02:17 AM

OK, I finally got apcupsd running and to connect to my Back-UPS Pro 1100VA (BP1100) today.

Used a 940-0024C cable (haven't tried it with the serial to USB converter yet).

The  apcupsd configuration that worked was "UPSCABLE 940-0024C", "UPSTYPE apcsmart", and "DEVICE COM1".

Apcupsd recognized the ups as a "BACK-UPS PRO 1000", the cable as a "Custom Cable Smart", and the driver as "APC Smart UPS (any)".

I'll try the serial to USB adapter with the 940-0024C (and maybe the apcupsd "Smart-Custom" and a "Simple-Custom" cables also) this weekend and provide an update then.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 04:27 AM . Last Modified: β€Ž2024-03-05 02:17 AM

0 Likes
0
2441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:27 AM . Last Modified: β€Ž2024-03-05 02:17 AM

I never could get the serial to USB converter to work. Made and tried both the apcupsd "Smart-Custom" and a "Simple-Custom" cables. The "Smart-Custom" serial cable with the apcupsd "UPSTYPE apcsmart" setting works the best. Tested this configuration and it notified me when it was on battery, notified me again when it hit low battery, then shut-down my PC cleanly and turned off.

Thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 04:27 AM . Last Modified: β€Ž2024-03-05 02:17 AM

0 Likes
0
2441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:27 AM . Last Modified: β€Ž2024-03-05 02:17 AM

I am trying to get an old Back-UPS Pro 1100VA (BP1100) to communicate through the serial port to a Windows 7 box. I'm using a 940-0024C cable. I tried PowerChute Personal V3.0.2 but it says it can't find the UPS.

Any suggestions?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 04:27 AM . Last Modified: β€Ž2024-03-05 02:17 AM

0 Likes
0
2442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 04:27 AM . Last Modified: β€Ž2024-03-05 02:17 AM

Thanks for the tips, yesterday I repair my old UPS "APC Back-UPS PRO 650", I changed all the capacitors, its 6 TO-220 Transistors, the adjust voltage IC, and the 4 relays, this UPS uses the cable 940-0095B, well I have installed Windows 8.1 Pro on my HP Compaq nx7400 old laptop with its docking with serial port, the Apcupsd daemon, my monitor AOC LM929 19 inches and works great together, I'm so happy because I can access to the UPS readings and now I have an autonomy for 65 minutes for my laptop and my monitor with this UPS. Thank you very much for the settings. πŸ™‚

  • Tags:
  • 650
  • apc
  • back-ups
  • pro
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore