PowerChute PE no shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute PE no shutdown
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

0 Likes
8
3079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

PowerChute PE no shutdown

i've simulate blackout on my Back-UPS 800VA (BX800CI-MS), using PowerChute Personal Edition 3.0.2 (conect via USB), on Win7 Ultimate 64bit.

disable hybrid sleep and hibernation, setting runtime > keep my computer (shutdown my computer) > 5 min.

nothing happens, only completely blackout without safe system shutdown my computer.

did i miss something or misconfiguration ??

thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:28 AM . Last Modified: ‎2024-03-05 02:16 AM

0 Likes
0
3079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:28 AM . Last Modified: ‎2024-03-05 02:16 AM

hi,

on first test to hibernate, it failed to hibernate though PowerChute hibernate pop-up show, because my windows is locked instead hibernate, so i fix it with the following step :

  • CMD > DISKPART > AUTOMOUNT ENABLE > EXIT > REBOOT

after that :

  • if hibernate on = PowerChute hibernates my computer ;
  • if hibernate off = PowerChute shutdown my computer properly .

and its solved this problem.

thanks.

MP

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

0 Likes
0
3079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

this article (screenshot attached) came up when i click help icon on runtime menu...

  • on image 1, below "Keep my computer...", it says "Shutdown my computer when the time..."
  • on image 2, point 4, it says "(If hibernation is disabled, shutdown begins.)"
  • on image 3, "Warning: ... automatically shutdown."

this nice feature is the main reason i'm using APC/PowerChute, i dont like to hibernate smile.

thanks.

[MP]

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

0 Likes
0
3079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

how to verifiy ?? like this ?? computer + monitor > surge outlets > back-ups .. usb (computer > backups)

yes, the battery successfully run my computer several minutes until blackout completely, without shutdown my computer

and yes again, when install PowerChute, it enables hibernate, but i disable it again (hybrid sleep off, hibernate off), because of what i read, hibernate off = powerchute will shutdown my computer..

thanks, sry for my english

smile

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

0 Likes
0
3079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

i've simulate blackout on my Back-UPS 800VA (BX800CI-MS), using PowerChute Personal Edition 3.0.2 (conect via USB), on Win7 Ultimate 64bit.

disable hybrid sleep and hibernation, setting runtime > keep my computer (shutdown my computer) > 5 min.

nothing happens, only completely blackout without safe system shutdown my computer.

did i miss something or misconfiguration ??

thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

0 Likes
0
3079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

Can you verify that you plugged your computer into the Battery Back UP + Surge outlets and not just surge only outlets?

Does the UPS run on battery successfully for several minutes and your computer stays running or is the problem as soon as the UPS switches to battery, the computer turns off?

When you install PowerChute, I believe it enables hibernation - you say you disabled it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

0 Likes
0
3079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:17 AM

When you disable hibernation does PowerChute record the power outage? Also, how much runtime does PowerChute report is available?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:16 AM

0 Likes
0
3079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:27 AM . Last Modified: ‎2024-03-05 02:16 AM

is this the record ?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:28 AM . Last Modified: ‎2024-03-05 02:16 AM

0 Likes
0
3079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:28 AM . Last Modified: ‎2024-03-05 02:16 AM

Hi,

From the command prompt enable hibernation. The command is  powercfg.exe /hibernate on. Test PowerChute to be sure the system shuts down / hibernates. After the test you can disable hibernation from the command prompt (powercfg.exe /hibernate off) and then test PowerChute to verify the system powers down.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:28 AM . Last Modified: ‎2024-03-05 02:16 AM

0 Likes
0
3080
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:28 AM . Last Modified: ‎2024-03-05 02:16 AM

hi,

on first test to hibernate, it failed to hibernate though PowerChute hibernate pop-up show, because my windows is locked instead hibernate, so i fix it with the following step :

  • CMD > DISKPART > AUTOMOUNT ENABLE > EXIT > REBOOT

after that :

  • if hibernate on = PowerChute hibernates my computer ;
  • if hibernate off = PowerChute shutdown my computer properly .

and its solved this problem.

thanks.

MP

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore