Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Connect HP 252663-D75 Modular Power DIstrobution Units to Symmetra LX?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3006:59 AM. Last Modified: 2024-03-0711:42 PM
From looking at HP's site this distribution unit's input requirements are: Input: 3.6m Attached Input cord, Non-NEMA Locking CS8265C, 50A. APC does not have any type of receptacle for this plug. You would either need to swap the input plug on the power distribution units to something smaller like a 30 amp plug, ie L6-30. Doing this would in turn downgrade the capacity of the PDU's to 30 amps vs. the 50 amps the device appears to be capable of pulling. I think the best option would be to have someone hardwire the output of the UPS to accomodate for the CS8265C plugs. An electrician can create a distribution panel with whichever outlets you desire to connect other devices as well. This would allow you to take advantage of the full capacity of your PDU's.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3006:59 AM. Last Modified: 2024-03-0711:42 PM
From looking at HP's site this distribution unit's input requirements are: Input: 3.6m Attached Input cord, Non-NEMA Locking CS8265C, 50A. APC does not have any type of receptacle for this plug. You would either need to swap the input plug on the power distribution units to something smaller like a 30 amp plug, ie L6-30. Doing this would in turn downgrade the capacity of the PDU's to 30 amps vs. the 50 amps the device appears to be capable of pulling. I think the best option would be to have someone hardwire the output of the UPS to accomodate for the CS8265C plugs. An electrician can create a distribution panel with whichever outlets you desire to connect other devices as well. This would allow you to take advantage of the full capacity of your PDU's.
This is a heading
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.