Configure PCNS 4.2 to Shutdown VM and ESXi hosts after 1 hour running on battery mode.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Configure PCNS 4.2 to Shutdown VM and ESXi hosts after 1 hour running on battery mode.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:41 PM . Last Modified: ‎2024-03-12 01:12 AM

0 Likes
3
1125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:41 PM . Last Modified: ‎2024-03-12 01:12 AM

Configure PCNS 4.2 to Shutdown VM and ESXi hosts after 1 hour running on battery mode.

Hi support,

Good day. I have APC Smart UPS 2200 with NMC configured, and the connection is established fine from UPS to my vCenter (with 2 ESXi hosts).

I can login to my PCNS agent installed in my vMA, and configured the "Virtual Machine Startup / Shutdown" which is default 120 seconds for both, and "vCenter Server VM Shutdown" for 240 seconds which is default settings also.

There is one question from me. Let's say there is power interruption and the UPS needs to operate in battery mode (currently can last for 1h 40 min). Is it possible to configure the UPS to operate in battery mode for 1 hour and followed by gracefully shutdown the VM and ESXi hosts? 

Thank you.

Best regards,

Kong

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:42 PM . Last Modified: ‎2024-03-12 01:12 AM

0 Likes
0
1126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:42 PM . Last Modified: ‎2024-03-12 01:12 AM

Hi,

The screenshot provided is the web interface for the network management card not PowerChute. To log into PowerChute you need the ip address of the system it is running on Example http://192.168.1.10:6547 Once logged in go to Configure Event - UPS on Battery. Select Shutdown - Enable Shutdown and enter 3600 seconds. 

See attached video

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:42 PM . Last Modified: ‎2024-03-12 01:12 AM

0 Likes
0
1126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:42 PM . Last Modified: ‎2024-03-12 01:12 AM

Hi,

Configure the On Battery event in the PowerChute interface and set the delay to 3600 seconds (1 hour). If the UPS runs on battery for longer than 1 hour PowerChute will start the shutdown process. When the process starts PowerChute will command the VMs and any Vapps down, Then vCenter server will be commanded down and finally the hosts. If left at the defaults settings the VM/Vapp power down delay is 120 seconds, then vCenter will power down which has a default delay of 240 seconds. After the 120 +240 second delays the hosts power down. 

See Application Note 180 http://www.apc.com/salestools/SJHN-92FLU8/SJHN-92FLU8_R6_EN.pdf?sdirect=true for a description of the VMware shutdown process similar to your is on page 4. 

I also suggest you read the User's Guide. http://www.apc.com/salestools/PMAR-9DNLQK/PMAR-9DNLQK_R3_EN.pdf?sdirect=true

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:42 PM . Last Modified: ‎2024-03-12 01:12 AM

0 Likes
0
1126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:42 PM . Last Modified: ‎2024-03-12 01:12 AM

Hi Bill,

Thanks for the reply. But I'm not sure whether I'm in the correct page of PowerChute interface, and where to configure the shutdown delay of 3600 seconds (1 hour). I can see the something like in the following screenshot.

Please advise.

Thank you.

Best regards,

Kong

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:42 PM . Last Modified: ‎2024-03-12 01:12 AM

0 Likes
0
1127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:42 PM . Last Modified: ‎2024-03-12 01:12 AM

Hi,

The screenshot provided is the web interface for the network management card not PowerChute. To log into PowerChute you need the ip address of the system it is running on Example http://192.168.1.10:6547 Once logged in go to Configure Event - UPS on Battery. Select Shutdown - Enable Shutdown and enter 3600 seconds. 

See attached video

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of