Compensating for a high input voltage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Compensating for a high input voltage
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

0 Likes
11
5204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

Compensating for a high input voltage

We've been receiving these for a short time so I'd like to ask whether it is safe to increase the 'high transfer' setting.

At the moment the high transfer setting is set to 250, but I'm seeing 252 in the logs

Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:46 PM . Last Modified: ‎2024-03-06 10:39 PM

0 Likes
0
5200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:46 PM . Last Modified: ‎2024-03-06 10:39 PM

Western power just called to say they are going to drop the voltage by 6v to fix this issue with it going to the limit all the time. Amazing no one else has noticed this!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

0 Likes
0
5200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

Hi,

What model UPS do you have? I assume you are in Europe and the normal voltage should be 230. Most of our UPS are designed to correct for over voltage by trimming instead of switching to battery. If the UPS is trimming the voltage you are fine if the UPS is switching to battery then you should contact the utility company and get the voltage issue resolved. you should not continually allowing high voltage through to the attached equipment. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

0 Likes
0
5200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

It's a 3000XL and we're in the UK, so 230V.

The logs are not reporting switching to Battery, just compensating so am I right saying it is trimming the voltage?

We are in discussion with the utility company but I need to know if the 252v is still within safe limits of the UPS

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

0 Likes
0
5200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

Hi,

On 2/16/2016 4:55 AM, Mark said:

The logs are not reporting switching to Battery, just compensating so am I right saying it is trimming the voltage?

Yes.

On 2/16/2016 4:55 AM, Mark said:

We are in discussion with the utility company but I need to know if the 252v is still within safe limits of the UPS

Yes. The UPS will continue to trim the incoming voltage until it either is corrected or increases 12 percent beyond the high voltage transfer point and at that point the UPS will switch to battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

0 Likes
0
5200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

253 volts is still within the 10% of 230v so the UPS is fine, infact mine lives around that point. Western power collected the voltage monitoring device today as I kept getting email alerts at 255 volts in the middle of the night as the UPS was trimming the incoming, sods law that I never got an alarm during the weeks monitoring. Even the WP engineer said he wouldn't be happy living with it near the 10% limit. I doubt they will do anything. Maybe they will swap me to another phase as my house has 3 phase.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

0 Likes
0
5200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

That's our issue, we keep getting these emails and funnily enough I'm pretty sure ours is Western Power too...we only started to see these notifications mid August last year and although we could create a rule on the mailbox to move them, I'd prefer to see things as and when situations arise.

What do you do Gareth?

Is the answer just to adjust the high transfer setting to 253V?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

0 Likes
0
5200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

mine is at 257 now as it was still being tripped at 255, call WP and tell them this is happening and they will setup a monitor, once they confirm it they can sort it.

Got to wait and see what they say as they only collected it yesterday.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:39 PM

0 Likes
0
5200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:39 PM

Yeah we've been in discussion with them already.

One of our issues it that it sounds like they want to turn the power off to the building to install the Monitor.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:39 PM

0 Likes
0
5200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:39 PM

Probably a jobsworth, we had an old chap who used common sense and didn't shut down the power to install/remove

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:39 PM

0 Likes
0
5200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:39 PM

I've set the high transfer to 257 to see if we stop getting the email notifications.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:46 PM . Last Modified: ‎2024-03-06 10:39 PM

0 Likes
0
5200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:46 PM . Last Modified: ‎2024-03-06 10:39 PM

I got phoned back with the expected results, didn't go above 10% but he didn't dismiss it, instead he said they are going to fit the monitor at the substation as we are a couple of streets away so those near the substation will probably be going over the 10%, once they have had it in for a week he will call me back to let me know if they are going to trim the voltage.

They way I see it is the fact it is at minimum 242 volts so they can knock 10 volts off and all will be good. And now back to waiting!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:46 PM . Last Modified: ‎2024-03-06 10:39 PM

0 Likes
0
5201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:46 PM . Last Modified: ‎2024-03-06 10:39 PM

Western power just called to say they are going to drop the voltage by 6v to fix this issue with it going to the limit all the time. Amazing no one else has noticed this!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of