Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Unexpected "Turned off for a defined period of time" on Symmetra RM w/ AP9631

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Unexpected "Turned off for a defined period of time" on Symmetra RM w/ AP9631
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
143
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

0 Likes
4
2896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

Unexpected "Turned off for a defined period of time" on Symmetra RM w/ AP9631

I was awakened due to an unexpected power outage in my server room. When I got to the server room, all indications on the UPS were normal and systems were beginning to turn back on as the UPS had decided to turn its output back on.

The event log contains "UPS: Turned off for a defined period of time in response to a software command, or off while waiting for input power to return to normal. 0x0115" Nobody did anything to the UPS - we were all (including the cat!) asleep at the time.

I am attaching a censored event.log to this message, which shows that the NMC2 has been up for 22 days and that there isn't anything odd in the logs. I removed a bunch of stuff between the last self-test and 24 hours before today's fault. The ftp login/logout is an automated config polling script which I've been running on hundreds of APC gizmos for over a decade, and which was last modified over 3 years ago. So that shouldn't have anything to do with it.

If any of the APC folks here want the complete debug file, just add me as a friend so I can PM you, and I'll send a link.

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

0 Likes
0
2895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

Nope. Nothing was changed on it recently (the last change was about 3 weeks earlier, upgrading to 6.4.0 on the NMC). The unit is polled every 5 minutes via SNMP (the only community is read-only) and hourly via FTP (which only does a single GET). There is a serial cable connecting it to a Cisco router's terminal server card, but that has been connected for several years (current configuration) and more than 5 years before that on a different Cisco router.

Unfortunately, I expect that the Symmetra RM6K is a mature product and there aren't going to be any changes to functionality (particularly as the firmware is in the microcontrollers and not field-upgradable). For future products, it would be great to have the reporting enhanced to say "Power off by NMC", "by serial command", "by simple signalling", etc. - with something like that, it should be possible to determine what caused it.

I believe there is an undocumented serial command to get debugging info out of the SYMIM3. If that info might have a clue as to what happened, just let me know what commands I should send to the UPS and I'll report back with the output. The SYMIM3 has pretty recent firmware - 226/143.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

0 Likes
0
2895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

Terry, 

Do you have the information from the "Logging" menu on the power view to see how the RM itself reported this? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

0 Likes
0
2895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

Quite a lot of stuff:

03:39:21 On Batt
03:39:31 On Line
03:39:43 UPS Turned Off
03:39:43 UPS Rebooting
03:39:49 UPS Into Bypass
03:39:49 UPS Reboot Complete
03:39:51 UPS Turned On
03:39:54 UPS Out of Bypass
03:39:54 On Line

The self-test passed on the 6th is the entry before that. Apparently my Powerview is in a different time zone foot-in-mouth. None of the 7 other APC units here (including 2 Matrix, so looking at the whole 208V) reported any power issues that night, so I'm not sure why the RM logged an "On Batt" event.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

0 Likes
0
2895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

Pretty strange. Not a whole lot to go on. Do you have anything set up to do graceful shutdowns of the system? The power view states it went through a reboot process as you can see. So it seems to have received a command from somewhere to do this (SNMP, serial, etc). 

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

0 Likes
0
2896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:45 PM . Last Modified: ‎2024-03-06 10:40 PM

Nope. Nothing was changed on it recently (the last change was about 3 weeks earlier, upgrading to 6.4.0 on the NMC). The unit is polled every 5 minutes via SNMP (the only community is read-only) and hourly via FTP (which only does a single GET). There is a serial cable connecting it to a Cisco router's terminal server card, but that has been connected for several years (current configuration) and more than 5 years before that on a different Cisco router.

Unfortunately, I expect that the Symmetra RM6K is a mature product and there aren't going to be any changes to functionality (particularly as the firmware is in the microcontrollers and not field-upgradable). For future products, it would be great to have the reporting enhanced to say "Power off by NMC", "by serial command", "by simple signalling", etc. - with something like that, it should be possible to determine what caused it.

I believe there is an undocumented serial command to get debugging info out of the SYMIM3. If that info might have a clue as to what happened, just let me know what commands I should send to the UPS and I'll report back with the output. The SYMIM3 has pretty recent firmware - 226/143.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore