Compensating for a high input voltag - Smart-UPS X 3000

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Compensating for a high input voltag - Smart-UPS X 3000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-18 12:48 AM

0 Likes
3
1868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-18 12:48 AM

Compensating for a high input voltag - Smart-UPS X 3000

Hello,

since the 22nd of December we are getting those error messages from our UPS in England.

The input is usually in the range of 240-244V and now it is between 249V to 255V.

The Overvoltage also only appears to be at daytime:

lWkpDJdPmVkVp6xn0MTi5w%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pnglWkpDJdPmVkVp6xn0MTi5w%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Should I contact the Power-Provider and can the USV handle that much overvoltage?

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-18 12:47 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-18 12:47 AM

I had this and 10% is overloading a fair bit of kit designed for 230v and will cause things to breakdown faster that having a stable voltage. I had a job getting my provider to get this sorted, in the end they fitted a monitor at home that showed it was always close or at the 10% so they moved the monitor to the substation and that went over the 10%, they turned the voltage down and all is good again. Your UPS logs will be a good start to get them to take notice.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 3
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-18 12:47 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-18 12:47 AM

Being in the US, our split phase voltages are often in such a high range of even 250 VAC plus.  However, usually these voltages are near an energy source (solar panels, wind, etc.).  As I understand the "normal" voltage of single phase European power is 208 VAC, so your voltages would seem quite extreme - or is the UK actually higher??

As to the UPS:

The SU and SUA 3000 (and SMT?) "high voltage" units that I've used are not configurable to 240 VAC and will essentially "compensate" for such high voltages continuously.  This is because they use massive transformers with specific winding taps.  Maybe an APC tech can tell you if long term use at 240 VAC is damaging - I've not seen any signs of damage using them continuously in the US.

The SMX 3000 unit can be configured to 240 VAC as the "normal" voltage and will not show such error messages.  These units are "transformer-less" (at least for the line voltages) and can be easily configured electronically for just about any voltages within the limits of design.

Voidstar - please correct me if any miss-statementssealed.

Mark

  

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-18 12:47 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-18 12:47 AM

Hi PANKL,

EU voltages are 230V +/- 10%, so 207-253V. So:

 - You may want to check your UPS's "output limits" setting (under Power Settings) to make sure it will accept the entire 207-253V range.

 - When the voltage exceed the output limits setting, the UPS will handle it fine but will automatically drop the voltage to protect attached equipment. That may or may not be necessary depending on the equipment. Either way, you'll just get a warning "Compensating for a high input voltage". If the voltage exceeds what the UPS can handle (unlikely -- that's really high), it'll go to battery.

 - 255V seems outside the standard voltage range. It might warrant double-checking with a voltmeter and calling the power provider. It might be that they're running the voltage high to lower current during times of peak demand.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-18 12:47 AM

0 Likes
0
1867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-18 12:47 AM

I had this and 10% is overloading a fair bit of kit designed for 230v and will cause things to breakdown faster that having a stable voltage. I had a job getting my provider to get this sorted, in the end they fitted a monitor at home that showed it was always close or at the 10% so they moved the monitor to the substation and that went over the 10%, they turned the voltage down and all is good again. Your UPS logs will be a good start to get them to take notice.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of