Causes of frequently power modules fault in Symmetra PX series

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Causes of frequently power modules fault in Symmetra PX series
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 06:01 AM . Last Modified: ‎2024-03-19 12:23 AM

0 Likes
3
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:01 AM . Last Modified: ‎2024-03-19 12:23 AM

Causes of frequently power modules fault in Symmetra PX series

Dear Team

I just want to confirm that

  1. Why power modules are gone faulty in symmetra PX series frequently.
  2. What is the maximum life of SYPM10KH if one day switching (Online to On battery operation) is 10 to 16 times

Regards

Mukhtar

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 06:01 AM . Last Modified: ‎2024-03-19 12:23 AM

0 Likes
0
2078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:01 AM . Last Modified: ‎2024-03-19 12:23 AM

I mean the power module we are using are 8 to 9 years old, its daily switching ratio 16 times approx. And every component have life specially relays and capacitors. The unit SYCF80KH is fully populated (9 Power modules) and after some days power module gone faulty.

When fault occurred UPS power view red light of failure lit with beep sound. Shows power module fault exist.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:01 AM . Last Modified: ‎2024-03-19 12:23 AM

0 Likes
0
2078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:01 AM . Last Modified: ‎2024-03-19 12:23 AM

So are you saying that 8-9 year old modules are failing, and then you reset them, and then they fail a few days later?

While the design life of a PX Power Module is 10 years, various factors (environment, power issues, etc) can either increase or decrease the actual lifetime that you see.

If I am correct in what I said above about them failing and you're resetting them, then perhaps because of all the power issues they are failing a little bit earlier than 10 years? Or did I misunderstand?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:01 AM . Last Modified: ‎2024-03-19 12:23 AM

0 Likes
0
2078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:01 AM . Last Modified: ‎2024-03-19 12:23 AM

Hello,

  • Can you define "frequently" and what type of faults do you see?
  • For your second question, we don't have that test data.

This might be something that if you're seeing failures that you believe are pre-mature that you discuss the failures with your local technical support that might require logs, detailed set up information, finding out what "faults" are occurring and going from there.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 06:01 AM . Last Modified: ‎2024-03-19 12:23 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:01 AM . Last Modified: ‎2024-03-19 12:23 AM

I mean the power module we are using are 8 to 9 years old, its daily switching ratio 16 times approx. And every component have life specially relays and capacitors. The unit SYCF80KH is fully populated (9 Power modules) and after some days power module gone faulty.

When fault occurred UPS power view red light of failure lit with beep sound. Shows power module fault exist.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of