APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-27 11:56 PM . Last Modified: ‎2024-03-18 11:44 PM
i have move tO live in Indonesian country, currently i have ups apc sua 1000xl. When i plugged the power cords tO the outlet power i got the led of site wiring fault become blink and stay tO red. in the first sign i Know it could be the voltage range probably caused the problem. So i try tO buy a transformer voltage stabilizher which is same brand apc le 1200i. but when i try tO use it i still have the red light from led of site wiring fault. I am confused right now because i have follow the guideline about voltage range problem.
fYi:indonesian voltage range is 220-230v. My ups is for american voltage range Which is 110va.
Is anyone here can help me tO solve the problem? many thanks tO try to help me.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-27 11:56 PM . Last Modified: ‎2024-03-18 11:44 PM
Yes, it will work if you somehow feed your North America UPS 110-120V using a transformer to step down 230V to 110-120V. It won't work without something like that is what I meant. At the end of the day, the UPS requires 110/120V so if you can provide that, it will be fine.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-27 11:56 PM . Last Modified: ‎2024-03-18 11:44 PM
Hi,
Site wiring fault is explained here. This link would also apply to Smart-UPS: http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA158817
Site wiring fault is more to indicate a wiring issue with the outlet your UPS is plugged into, not so much a voltage issue.
Note also a UPS designed for North America won't work properly when fed 220-230V. You'll need to get a UPS that is designed for that operating voltage range. That wouldn't relate to the site wiring fault.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-27 11:56 PM . Last Modified: ‎2024-03-18 11:44 PM
Hello Angela,
thanks to try tO help ke WITh This problem. According tO your explaination. 'Won't work properly', is it still not working even if i use step-up/step-Down/ voltage transformator tO stabilized THe current voltage to the UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-27 11:56 PM . Last Modified: ‎2024-03-18 11:44 PM
Yes, it will work if you somehow feed your North America UPS 110-120V using a transformer to step down 230V to 110-120V. It won't work without something like that is what I meant. At the end of the day, the UPS requires 110/120V so if you can provide that, it will be fine.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.