Smart-UPS 3000 Model: DLA3000RM2U

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 3000 Model: DLA3000RM2U
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:55 PM . Last Modified: ‎2024-03-18 11:44 PM

0 Likes
4
872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:55 PM . Last Modified: ‎2024-03-18 11:44 PM

Smart-UPS 3000 Model: DLA3000RM2U

I am looking for insight on this unit as I have no manual. One of the batteries require replacement, so I would like to get in depth information before proceeding. We have PowerChute Business Edition 9.0.1 at the moment. Could someone assist with the questions below please?

1. Can this units batteries be hot swapped?

2. Are there any defined steps that should be taken, in order to "reset" the unit once the new batteries are installed?

Thank you in advance.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:56 PM . Last Modified: ‎2024-03-18 11:44 PM

0 Likes
0
872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:56 PM . Last Modified: ‎2024-03-18 11:44 PM

I restarted the server itself and the self test is in progress.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:55 PM . Last Modified: ‎2024-03-18 11:44 PM

0 Likes
0
872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:55 PM . Last Modified: ‎2024-03-18 11:44 PM

  1. Yes, batteries are hot swappable. Just be advised that when they are removed, you have no battery back up for that few minutes they are removed if there is a power blip or event.
  2. Let the UPS charge for at least 8 hours. You'll want to run a UPS self test after the charge reaches 100% to clear any replace battery alarms and after the battery is charged up. Then, you should check your available runtime to make sure it updates within the PowerChute software. If it does not, issue a runtime calibration via PowerChute which will discharge the UPS to 10-20% capacity (not affecting your load) and then charge back up to recalculate the runtime. Also, update the UPS battery replacement date within PowerChute so you know when it was last replaced.
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:55 PM . Last Modified: ‎2024-03-18 11:44 PM

0 Likes
0
872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:55 PM . Last Modified: ‎2024-03-18 11:44 PM

Thank you for the information, I appreciate it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:56 PM . Last Modified: ‎2024-03-18 11:44 PM

0 Likes
0
872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:56 PM . Last Modified: ‎2024-03-18 11:44 PM

Good Morning,

The new battery has been installed and all went smooth. However, I now get an error using the PowerChute Business edition. When trying to perform a self-test, it produces an error "Set request failed, Please try again". It will not allow me to make any changes. The USB cable is attached and I have tried restarting the APC PBE Agent / Server which did not correct the issue.

uB%2BIDpHIfWPDc%2BKtGhFc2Q%3D%3D.jpeguB%2BIDpHIfWPDc%2BKtGhFc2Q%3D%3D.jpeg

Any ideas on how this can be resolved?

Thank you in advance.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:56 PM . Last Modified: ‎2024-03-18 11:44 PM

0 Likes
0
873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:56 PM . Last Modified: ‎2024-03-18 11:44 PM

I restarted the server itself and the self test is in progress.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of