I am looking for insight on this unit as I have no manual. One of the batteries require replacement, so I would like to get in depth information before proceeding. We have PowerChute Business Edition 9.0.1 at the moment. Could someone assist with the questions below please?
1. Can this units batteries be hot swapped?
2. Are there any defined steps that should be taken, in order to "reset" the unit once the new batteries are installed?
Thank you in advance.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:56 PM . Last Modified: 2024-03-18 11:44 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:56 PM . Last Modified: 2024-03-18 11:44 PM
I restarted the server itself and the self test is in progress.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:55 PM . Last Modified: 2024-03-18 11:44 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:55 PM . Last Modified: 2024-03-18 11:44 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:55 PM . Last Modified: 2024-03-18 11:44 PM
Thank you for the information, I appreciate it.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:56 PM . Last Modified: 2024-03-18 11:44 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:56 PM . Last Modified: 2024-03-18 11:44 PM
Good Morning,
The new battery has been installed and all went smooth. However, I now get an error using the PowerChute Business edition. When trying to perform a self-test, it produces an error "Set request failed, Please try again". It will not allow me to make any changes. The USB cable is attached and I have tried restarting the APC PBE Agent / Server which did not correct the issue.
uB%2BIDpHIfWPDc%2BKtGhFc2Q%3D%3D.jpeg
Any ideas on how this can be resolved?
Thank you in advance.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:56 PM . Last Modified: 2024-03-18 11:44 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:56 PM . Last Modified: 2024-03-18 11:44 PM
I restarted the server itself and the self test is in progress.