Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Cannot communicate with UPS after Update firmware AP9617 with Network Manag

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Cannot communicate with UPS after Update firmware AP9617 with Network Manag
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:51 AM . Last Modified: ‎2024-03-07 02:31 AM

0 Likes
6
2639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:51 AM . Last Modified: ‎2024-03-07 02:31 AM

Cannot communicate with UPS after Update firmware AP9617 with Network Manag

I have a smart ups 3000 with a network card AP9617 before the firmware update works perfectly with the APC Network Shutdown application.
After Upgrading the Firmware AP9617 network card can not make it work with the software.
he error to give the network card in the UPS lost communications options
The firmware version is v3.5.8.
The application runs on Windows 2003 standard SP2
I Need help to solve this problem.
Thank you very much.

Message was edited by: Giux

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:52 AM . Last Modified: ‎2024-03-07 02:23 AM

0 Likes
0
2638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:52 AM . Last Modified: ‎2024-03-07 02:23 AM

That's good to hear Giux, if you have any more problem please do not hesitate to contact us.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:51 AM . Last Modified: ‎2024-03-07 02:31 AM

0 Likes
0
2638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:51 AM . Last Modified: ‎2024-03-07 02:31 AM

Hi JonPro,
Is working, thank you very much for your help.
king regards
Giux

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:51 AM . Last Modified: ‎2024-03-07 02:31 AM

0 Likes
0
2638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:51 AM . Last Modified: ‎2024-03-07 02:31 AM

I have a smart ups 3000 with a network card AP9617 before the firmware update works perfectly with the APC Network Shutdown application.
After Upgrading the Firmware AP9617 network card can not make it work with the software.
he error to give the network card in the UPS lost communications options
The firmware version is v3.5.8.
The application runs on Windows 2003 standard SP2
I Need help to solve this problem.
Thank you very much.

Message was edited by: Giux

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:52 AM . Last Modified: ‎2024-03-07 02:31 AM

0 Likes
0
2638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:52 AM . Last Modified: ‎2024-03-07 02:31 AM

Hello Giux,

Based from the screenshots that you have provided there could be something wrong with the firmware that was loaded on your card. Would it be possible for you to provide the model and serial number of your UPS? Also, on your network management card's interface kindly click on the Administration tab and then choose General and then click on About. Once you are on the About page, please tell me what do you see under the Application part, if you are using a Smart-UPS it should be SUMX.

Again, if would help us if you'll be able to tell us what kind of Smart-UPS do you have. We'll be waiting for your response.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:52 AM . Last Modified: ‎2024-03-07 02:31 AM

0 Likes
0
2638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:52 AM . Last Modified: ‎2024-03-07 02:31 AM

Hello JonPro
I made a screenshot with the image displayed on the screen.
I have is Smart UPS 3000.

The configuration Network Card is:

Hardware Factory

Model Number: AP9617
Serial Number: JA0351044852
Hardware Revision: A10
Manufacture Date: 12/22/2003
MAC Address: 00 C0 B7 6C 23 FC
Management Uptime: 0 Days 3 Hours 59 Minutes


Application Module

Name: sy
Version: v3.5.8
Date: 11/05/2008
Time: 16:28:07


Thank you very much

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:52 AM . Last Modified: ‎2024-03-07 02:31 AM

0 Likes
0
2638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:52 AM . Last Modified: ‎2024-03-07 02:31 AM

Hi Giux,

Thank you for posting these information. Just like what I have suspected, the firmware that was loaded on the card is for our Symmetra(*sy*) units. To help you resolve the problem I highly recommend that you download the firmware that would work for your UPS which is SUMX (Smart-UPS and Matrix).

Please go to our APC download page --> [Download Page|http://www.apc.com/tools/download/index.cfm] and then on the first drop down box please choose Firmware Upgrades - Network Management Card. If done correctly you will be given a list of all the firmwares available for both the Network Management Card 1 and 2. I would like you to click on the SFSUMX358(Network Management Card v3.5.8 firmware executable for Smart UPS and Matrix w/ AP9617/8/9) download button, you might be asked to login first before you can download it so please do so. This is a self-extracting file and I suggest that you create a folder/director in which the files can be extracted.

To help you out, here is an APC Knowledge Base Article regarding firmware upgrade --> [please click here|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=768].

Goodluck and keep us posted.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:52 AM . Last Modified: ‎2024-03-07 02:23 AM

0 Likes
0
2639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:52 AM . Last Modified: ‎2024-03-07 02:23 AM

That's good to hear Giux, if you have any more problem please do not hesitate to contact us.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore