Can't see SUA1500RM2U in powerchute software

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can't see SUA1500RM2U in powerchute software
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:16 PM

0 Likes
6
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:16 PM

Can't see SUA1500RM2U in powerchute software

I just acquired a APC Smartups SUA1500RM2U and my powerchute software cannot recognize it with either the USB cable or the simple signaling serial cables. I have a Smartups SC1500 and that communicates fine. I have installed new batteries and bench tested it, and it works flawlessly. With the exception that it is not recognized in the powerchute software.

 

Thanks

Skip

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:15 PM

0 Likes
0
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:15 PM

Hi,

You cannot make any adjustments to a SUA Smart-UPS using a simple signaling cable. You will need the Smart signaling cable part number 940-0024 or 940-1524. Simple signaling is one way communications from UPS to the OS. Smart signaling is two way communications. 

With USB when attaching the cable under device manager you should see in Batteries and APC UPS. If that driver is loaded PowerChute should communicate with the Smart-UPS. If the driver is loaded and communication is not established you should click on the driver and reload it. Kbase FA164514 discusses loading USB drivers. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:16 PM

0 Likes
0
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:16 PM

Hi,

Are you connecting both UPS at the same time? If so that is not supported. Also, depending on the model Smart-UPS SC you may need to uninstall and reinstall PowerChute for it to recognize the SUA. When the SC is connected look in about what Agent version is installed?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:16 PM

0 Likes
0
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:16 PM

I don't have the smartups SC1500 on the network or connected to the PC with the powerchute software. Nothing is recognized when the SUA is connected. I tried both cables, but not together! It also is seen (USB) in the device manager in windows 7.

I don't have much experience with these APC's or this software but I am suprised that when the SC1500 was recognized and seemed to work well with the software, that the SUA1500RM2U was not recognized.

Also I connected (USB) the SUA1500 to my NAS server (synology) and it recognized it. That at least tells me the APC is communicating.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:16 PM

0 Likes
0
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:16 PM

Skip,

What is the OS and what version of the Powerchute installer are you runnng?

Note: Once you have connected a system to the SUA via USB to switch communication back to Serial comm you must reset the UPS.

To reset

1) Turn off and unplug UPS from wall
2) Press and hold the OFF button again
3) You may see a quick flash of the LED's and you should hear an audible "click" from the UPS.
4) Plug UPS back into the wall and turn UPS back on

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:15 PM

0 Likes
0
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:15 PM

Thanks Bill, I will give it a try when I get it loaded with new batteries

Skip

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:15 PM

0 Likes
0
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:15 PM

I have tried to reset this APC a number of times and tried individually each cable, the simple signaling cable with serial on one end and USB on the other and a standard USB cable connection.

Its kind of strange as I have an older DL3000RM3U and Smartups SC1500 and they communicates fine with the simple signaling cable. I am using a Windows 7 Ultimate OS and using the web agent on Powerchute Business Edition v9.0.3.604

I just want to silence the alarm when on battery!

 

Skip

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:15 PM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:28 AM . Last Modified: ‎2024-03-18 11:15 PM

Hi,

You cannot make any adjustments to a SUA Smart-UPS using a simple signaling cable. You will need the Smart signaling cable part number 940-0024 or 940-1524. Simple signaling is one way communications from UPS to the OS. Smart signaling is two way communications. 

With USB when attaching the cable under device manager you should see in Batteries and APC UPS. If that driver is loaded PowerChute should communicate with the Smart-UPS. If the driver is loaded and communication is not established you should click on the driver and reload it. Kbase FA164514 discusses loading USB drivers. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of