Can't get agent running. SMT1500

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can't get agent running. SMT1500
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
10
2377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

Can't get agent running. SMT1500

I have purchased a new Smart-UPS 1500 LCD (SMT1500) and have it hooked up to a Windows 2003 SBS w/ SP2 via USB. I downloaded the Powerchute 9.0 (5 node) and installed all 3 modules (agent, server, console), however, I am unable to get the agent service to run. I tried uninstalling all of the java versions on the server and installed the latest version thinking that would help, and reinstalled the agent, but no luck. I also uninstalled Mcafee Antivirus Enterprise 8.7 thinking that was blocking it.
The service shows as starting, even if i change from automatic to manual. I can't stop it.
I also can't access the web interface through http://127.0.0.1:3052/
In C:\Program Files\APC\PowerChute Business Edition\agent, I see an error log that shows the following which lead me to believe it may be a java issue?:

# A fatal error has been detected by the Java Runtime Environment:
#
# EXCEPTION_ACCESS_VIOLATION (0xc0000005) at pc=0x77bbb08c, pid=5952, tid=6052
#
# JRE version: 6.0_19-b04
# Java VM: Java HotSpot(TM) Client VM (16.2-b04 mixed mode windows-x86 )
# Problematic frame:
# C [msvcrt.dll+0x1b08c]
#
# If you would like to submit a bug report, please visit:
# http://java.sun.com/webapps/bugreport/crash.jsp
# The crash happened outside the Java Virtual Machine in native code.
# See problematic frame for where to report the bug.
#

--------------- T H R E A D ---------------

Current thread (0x0baa2c00): JavaThread "USB_UPS_DetectTimer" daemon [_thread_in_native, id=6052, stack(0x0cd00000,0x0ce00000)]

siginfo: ExceptionCode=0xc0000005, reading address 0x005f33ce

Registers:
EAX=0x005b1fd8, EBX=0x005f33ce, ECX=0x00030002, EDX=0x000033d0
ESP=0x0cdff834, EBP=0x0cdff850, ESI=0x005c33cc, EDI=0x00000000
EIP=0x77bbb08c, EFLAGS=0x00010246

Message was edited by: ss911der

Message was edited by: ss911der

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

No problems doing the system file checker.
The debug file in the apc agent folder shows the following:



Fri Jan 28 18:01:04 EST 2011: [MicroLinkDeviceTranslator.()]- added MicroLinkOutletSystem data model to DataModelRegistry
Fri Jan 28 18:01:04 EST 2011: [MicroLinkDeviceTranslator.()]- added UPSCapabilities data model to DataModelRegistry
Fri Jan 28 18:01:04 EST 2011: [MicroLinkBatterySystem.()]- There was an error while querying the device for FQUNs: com.apcc.m11.arch.CommunicationException: MicroLink engine has not been inited yet.
Fri Jan 28 18:01:04 EST 2011: [MicroLinkDeviceTranslator.()]- added UPSCapabilities data model to DataModelRegistry
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Normal Energy Usage Startup.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Country: US
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Weight Measurement being used: Imperial
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- User has supplied their own data: false
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Reporting Start Date: Wed Jan 26 00:00:00 EST 2011
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Reporting End Date: null
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- PCBE Install Date: Wed Jan 26 00:00:00 EST 2011
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- PCBE Agent last contacted APC Energy Usage Web Service on Date: Wed Jan 26 00:00:00 EST 2011
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- Error retriving Energy Usage Variable 'WebServiceURL' from Permanent Storage.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- ConfigEntry not found: EnergyUsage.WebServiceURL
- Fri Jan 28 18:01:05 EST 2011:Critical Exception class com.apcc.m11.arch.storage.StorageEntryException:ConfigEntry not found: EnergyUsage.WebServiceURL On Thread Thread[PCBE Agent Main Thread,5,main] Caught at EnergyUsageReporting.readFromPermanentStorage()[:]
Thrown at HashPermanentStorage.readData()[:]
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.configureWebServiceVariables()]- Setting Default (EnergyUsageWebServiceURL): Web Service URL: http://updates.apc.com/pcbe/energyusage/GetPCBEInfo.cfm?Country=US
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- Error retriving Energy Usage Variable 'WebServicePCBESleepSeconds' from Permanent Storage.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- ConfigEntry not found: EnergyUsage.WebServicePCBESleepSeconds
- Fri Jan 28 18:01:05 EST 2011:Critical Exception class com.apcc.m11.arch.storage.StorageEntryException:ConfigEntry not found: EnergyUsage.WebServicePCBESleepSeconds On Thread Thread[PCBE Agent Main Thread,5,main] Caught at EnergyUsageReporting.readFromPermanentStorage()[:]
Thrown at HashPermanentStorage.readData()[:]
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.configureWebServiceVariables()]- Setting Default (EnergyUsageWebServicePCBESleepSeconds): Amount of sleep time between contacting APC Web Service: 2628000 Seconds.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- Error retriving Energy Usage Variable 'WebServiceRetrySleep1Seconds' from Permanent Storage.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- ConfigEntry not found: EnergyUsage.WebServiceRetrySleep1Seconds
- Fri Jan 28 18:01:05 EST 2011:Critical Exception class com.apcc.m11.arch.storage.StorageEntryException:ConfigEntry not found: EnergyUsage.WebServiceRetrySleep1Seconds On Thread Thread[PCBE Agent Main Thread,5,main] Caught at EnergyUsageReporting.readFromPermanentStorage()[:]
Thrown at HashPermanentStorage.readData()[:]
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.configureWebServiceVariables()]- Setting Default (EnergyUsageWebServiceRetrySleep1Seconds): APC Web Service sleep time retry #1: 600 Seconds.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- Error retriving Energy Usage Variable 'WebServiceRetrySleep2Seconds' from Permanent Storage.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- ConfigEntry not found: EnergyUsage.WebServiceRetrySleep2Seconds
- Fri Jan 28 18:01:05 EST 2011:Critical Exception class com.apcc.m11.arch.storage.StorageEntryException:ConfigEntry not found: EnergyUsage.WebServiceRetrySleep2Seconds On Thread Thread[PCBE Agent Main Thread,5,main] Caught at EnergyUsageReporting.readFromPermanentStorage()[:]
Thrown at HashPermanentStorage.readData()[:]
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.configureWebServiceVariables()]- Setting Default (EnergyUsageWebServiceRetrySleep2Seconds): APC Web Service sleep time retry #2: 1800 Seconds.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- Error retriving Energy Usage Variable 'WebServiceRetrySleep3Seconds' from Permanent Storage.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- ConfigEntry not found: EnergyUsage.WebServiceRetrySleep3Seconds
- Fri Jan 28 18:01:05 EST 2011:Critical Exception class com.apcc.m11.arch.storage.StorageEntryException:ConfigEntry not found: EnergyUsage.WebServiceRetrySleep3Seconds On Thread Thread[PCBE Agent Main Thread,5,main] Caught at EnergyUsageReporting.readFromPermanentStorage()[:]
Thrown at HashPermanentStorage.readData()[:]
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.configureWebServiceVariables()]- Setting Default (EnergyUsageWebServiceRetrySleep3Seconds): APC Web Service sleep time retry #3: 3600 Seconds.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Duration since PCBE Agent last contacted APC Energy Usage Web Service (Days): 2
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Duration till PCBE Agent next contacts APC Energy Usage Web Service (Days): 27
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Duration since Agent last contacted APC Energy Usage Web Service has not expired. Therefore not contacting Web Service as part of startup.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting$APCEnergyUsageWebServiceChecker.run()]- PCBE Agent Energy Usage Web Service Checker Sleeping 2390335000 Milliseconds (27 Days) before contacting APC Energy Usage Web Service and checking for updates.
Fri Jan 28 18:01:06 EST 2011: [MicroLinkSlaveMonitorClient.()]- Version: 22(78EA31685F1CABBA2CADAF470A3DD69B)
Fri Jan 28 18:01:06 EST 2011: [Logger.error()]- USBTranslator.openDevice() - Failed: com.apcc.m11.components.MicroLinkPowerSource.protocols.usb.DeviceOpenException: Device ID reference is null
Fri Jan 28 18:01:06 EST 2011: [Logger.error()]- USBTranslator.openDevice() - Failed: com.apcc.m11.components.MicroLinkPowerSource.protocols.usb.DeviceOpenException: Device ID reference is null
Fri Jan 28 18:01:11 EST 2011: [IndependentPowerSource.get()]- get(.3.1.1.1)com.apcc.m11.components.MicroLinkPowerSource.Exceptions.NotInitializedException
Fri Jan 28 18:01:11 EST 2011: [MicroLinkSwitchedOutletGroup.()]- Could not initialise 'theOutletGroup' with: SOG1
Fri Jan 28 18:01:12 EST 2011: [BypassReasonState.processReasonByStatusRegister()]- Duplicate event or Invalid bitmask value for UPSStatus_BF

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

I have purchased a new Smart-UPS 1500 LCD (SMT1500) and have it hooked up to a Windows 2003 SBS w/ SP2 via USB. I downloaded the Powerchute 9.0 (5 node) and installed all 3 modules (agent, server, console), however, I am unable to get the agent service to run. I tried uninstalling all of the java versions on the server and installed the latest version thinking that would help, and reinstalled the agent, but no luck. I also uninstalled Mcafee Antivirus Enterprise 8.7 thinking that was blocking it.
The service shows as starting, even if i change from automatic to manual. I can't stop it.
I also can't access the web interface through http://127.0.0.1:3052/
In C:\Program Files\APC\PowerChute Business Edition\agent, I see an error log that shows the following which lead me to believe it may be a java issue?:

# A fatal error has been detected by the Java Runtime Environment:
#
# EXCEPTION_ACCESS_VIOLATION (0xc0000005) at pc=0x77bbb08c, pid=5952, tid=6052
#
# JRE version: 6.0_19-b04
# Java VM: Java HotSpot(TM) Client VM (16.2-b04 mixed mode windows-x86 )
# Problematic frame:
# C [msvcrt.dll+0x1b08c]
#
# If you would like to submit a bug report, please visit:
# http://java.sun.com/webapps/bugreport/crash.jsp
# The crash happened outside the Java Virtual Machine in native code.
# See problematic frame for where to report the bug.
#

--------------- T H R E A D ---------------

Current thread (0x0baa2c00): JavaThread "USB_UPS_DetectTimer" daemon [_thread_in_native, id=6052, stack(0x0cd00000,0x0ce00000)]

siginfo: ExceptionCode=0xc0000005, reading address 0x005f33ce

Registers:
EAX=0x005b1fd8, EBX=0x005f33ce, ECX=0x00030002, EDX=0x000033d0
ESP=0x0cdff834, EBP=0x0cdff850, ESI=0x005c33cc, EDI=0x00000000
EIP=0x77bbb08c, EFLAGS=0x00010246

Message was edited by: ss911der

Message was edited by: ss911der

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

If you have your OS install CD handy you may want to try a repair installation after you've removed Java, PCBE and run the registry cleaner.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

So, I tried replacing the .dll file in windows\system32 with a newer version, but with no success. Anyone know what the deal is with my situation?

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

Ok, I will run SFC and see what it finds. Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

I've installed the same version it was tested with, and used the APC java application to switch between different versions (latest version) of java. No luck. Any other suggestions? I am not giving up.

Message was edited by: ss911der

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

Do I need to open up a ticket with phone support? I need to get this resolved.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

No problems doing the system file checker.
The debug file in the apc agent folder shows the following:



Fri Jan 28 18:01:04 EST 2011: [MicroLinkDeviceTranslator.()]- added MicroLinkOutletSystem data model to DataModelRegistry
Fri Jan 28 18:01:04 EST 2011: [MicroLinkDeviceTranslator.()]- added UPSCapabilities data model to DataModelRegistry
Fri Jan 28 18:01:04 EST 2011: [MicroLinkBatterySystem.()]- There was an error while querying the device for FQUNs: com.apcc.m11.arch.CommunicationException: MicroLink engine has not been inited yet.
Fri Jan 28 18:01:04 EST 2011: [MicroLinkDeviceTranslator.()]- added UPSCapabilities data model to DataModelRegistry
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Normal Energy Usage Startup.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Country: US
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Weight Measurement being used: Imperial
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- User has supplied their own data: false
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Reporting Start Date: Wed Jan 26 00:00:00 EST 2011
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Reporting End Date: null
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- PCBE Install Date: Wed Jan 26 00:00:00 EST 2011
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- PCBE Agent last contacted APC Energy Usage Web Service on Date: Wed Jan 26 00:00:00 EST 2011
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- Error retriving Energy Usage Variable 'WebServiceURL' from Permanent Storage.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- ConfigEntry not found: EnergyUsage.WebServiceURL
- Fri Jan 28 18:01:05 EST 2011:Critical Exception class com.apcc.m11.arch.storage.StorageEntryException:ConfigEntry not found: EnergyUsage.WebServiceURL On Thread Thread[PCBE Agent Main Thread,5,main] Caught at EnergyUsageReporting.readFromPermanentStorage()[:]
Thrown at HashPermanentStorage.readData()[:]
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.configureWebServiceVariables()]- Setting Default (EnergyUsageWebServiceURL): Web Service URL: http://updates.apc.com/pcbe/energyusage/GetPCBEInfo.cfm?Country=US
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- Error retriving Energy Usage Variable 'WebServicePCBESleepSeconds' from Permanent Storage.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- ConfigEntry not found: EnergyUsage.WebServicePCBESleepSeconds
- Fri Jan 28 18:01:05 EST 2011:Critical Exception class com.apcc.m11.arch.storage.StorageEntryException:ConfigEntry not found: EnergyUsage.WebServicePCBESleepSeconds On Thread Thread[PCBE Agent Main Thread,5,main] Caught at EnergyUsageReporting.readFromPermanentStorage()[:]
Thrown at HashPermanentStorage.readData()[:]
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.configureWebServiceVariables()]- Setting Default (EnergyUsageWebServicePCBESleepSeconds): Amount of sleep time between contacting APC Web Service: 2628000 Seconds.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- Error retriving Energy Usage Variable 'WebServiceRetrySleep1Seconds' from Permanent Storage.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- ConfigEntry not found: EnergyUsage.WebServiceRetrySleep1Seconds
- Fri Jan 28 18:01:05 EST 2011:Critical Exception class com.apcc.m11.arch.storage.StorageEntryException:ConfigEntry not found: EnergyUsage.WebServiceRetrySleep1Seconds On Thread Thread[PCBE Agent Main Thread,5,main] Caught at EnergyUsageReporting.readFromPermanentStorage()[:]
Thrown at HashPermanentStorage.readData()[:]
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.configureWebServiceVariables()]- Setting Default (EnergyUsageWebServiceRetrySleep1Seconds): APC Web Service sleep time retry #1: 600 Seconds.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- Error retriving Energy Usage Variable 'WebServiceRetrySleep2Seconds' from Permanent Storage.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- ConfigEntry not found: EnergyUsage.WebServiceRetrySleep2Seconds
- Fri Jan 28 18:01:05 EST 2011:Critical Exception class com.apcc.m11.arch.storage.StorageEntryException:ConfigEntry not found: EnergyUsage.WebServiceRetrySleep2Seconds On Thread Thread[PCBE Agent Main Thread,5,main] Caught at EnergyUsageReporting.readFromPermanentStorage()[:]
Thrown at HashPermanentStorage.readData()[:]
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.configureWebServiceVariables()]- Setting Default (EnergyUsageWebServiceRetrySleep2Seconds): APC Web Service sleep time retry #2: 1800 Seconds.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- Error retriving Energy Usage Variable 'WebServiceRetrySleep3Seconds' from Permanent Storage.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.readFromPermanentStorage()]- ConfigEntry not found: EnergyUsage.WebServiceRetrySleep3Seconds
- Fri Jan 28 18:01:05 EST 2011:Critical Exception class com.apcc.m11.arch.storage.StorageEntryException:ConfigEntry not found: EnergyUsage.WebServiceRetrySleep3Seconds On Thread Thread[PCBE Agent Main Thread,5,main] Caught at EnergyUsageReporting.readFromPermanentStorage()[:]
Thrown at HashPermanentStorage.readData()[:]
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.configureWebServiceVariables()]- Setting Default (EnergyUsageWebServiceRetrySleep3Seconds): APC Web Service sleep time retry #3: 3600 Seconds.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Duration since PCBE Agent last contacted APC Energy Usage Web Service (Days): 2
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Duration till PCBE Agent next contacts APC Energy Usage Web Service (Days): 27
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting.()]- Duration since Agent last contacted APC Energy Usage Web Service has not expired. Therefore not contacting Web Service as part of startup.
Fri Jan 28 18:01:05 EST 2011: [EnergyUsageReporting$APCEnergyUsageWebServiceChecker.run()]- PCBE Agent Energy Usage Web Service Checker Sleeping 2390335000 Milliseconds (27 Days) before contacting APC Energy Usage Web Service and checking for updates.
Fri Jan 28 18:01:06 EST 2011: [MicroLinkSlaveMonitorClient.()]- Version: 22(78EA31685F1CABBA2CADAF470A3DD69B)
Fri Jan 28 18:01:06 EST 2011: [Logger.error()]- USBTranslator.openDevice() - Failed: com.apcc.m11.components.MicroLinkPowerSource.protocols.usb.DeviceOpenException: Device ID reference is null
Fri Jan 28 18:01:06 EST 2011: [Logger.error()]- USBTranslator.openDevice() - Failed: com.apcc.m11.components.MicroLinkPowerSource.protocols.usb.DeviceOpenException: Device ID reference is null
Fri Jan 28 18:01:11 EST 2011: [IndependentPowerSource.get()]- get(.3.1.1.1)com.apcc.m11.components.MicroLinkPowerSource.Exceptions.NotInitializedException
Fri Jan 28 18:01:11 EST 2011: [MicroLinkSwitchedOutletGroup.()]- Could not initialise 'theOutletGroup' with: SOG1
Fri Jan 28 18:01:12 EST 2011: [BypassReasonState.processReasonByStatusRegister()]- Duplicate event or Invalid bitmask value for UPSStatus_BF

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

I ran across that as well, but no luck.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

I tried firefox as well as IE. The agent service has a problem starting, so I didn't even bother trying on another pc.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

I have tried searching thru Google about this problem and I've chanced upon a person who said that what he did is uninstall JVM and run CCleaner. He then restarted the machine and reinstalled Java and the application that he intent to use.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore