Symmetra RM 6KVa in and out of bypass

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra RM 6KVa in and out of bypass
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:01 AM . Last Modified: ‎2024-03-08 05:02 AM

0 Likes
8
2120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:01 AM . Last Modified: ‎2024-03-08 05:02 AM

Symmetra RM 6KVa in and out of bypass

Unit passes self-test every 14 days, but between I see the following events in the logs. Prognosis?

01/22/2011 18:40:44 UPS: A battery charger fault no longer exists.
01/22/2011 18:40:39 UPS: A battery charger fault exists.

01/17/2011 06:40:06 UPS: No longer in bypass.
01/17/2011 06:40:02 UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.

01/16/2011 21:36:57 UPS: No longer in bypass.
01/16/2011 21:36:55 UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.

01/15/2011 15:56:56 UPS: No longer in bypass.
01/15/2011 15:56:53 UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.

01/13/2011 10:03:41 UPS: Passed a self-test.
01/13/2011 10:03:21 UPS: Started a self-test.


APP Module
Version: v3.7.2
AOS
Version: v3.7.3

Battery Capacity: 100.0 %
Runtime Remaining: 1 hour 1 minute
Nominal Battery Voltage: 120.0 VDC
Actual Battery Bus Voltage: 138.2 VDC

Last Battery Transfer: Due to software command or UPS's test control
Internal Temperature: 93.0°F
Runtime Remaining: 1 hour 2 minutes
Input Power
Input Voltage: 246.0 VAC
Input Frequency: 59.98 Hz
Output Power
Output Voltage: 211.2 VAC
Output Frequency: 59.99 Hz
Output Current: 01.3 Amps
Output Load kVA: 00.28 kVA
Output Watts at n+0: 019 %Watts
Output VA at n+0: 007 %VA
Fault Tolerance
Redundancy: n+1
Present kVA Capacity: 04.0 kVA




And a little history of events on this unit.


_12/01/2010 Batteries run down to 0% after power outage_
12/01/2010 15:13:30 UPS: A power module fault exists.

_12/02/2010 Replaced failed power module_
12/02/2010 00:59:24 UPS: A power module fault no longer exists.

_12/04/2010 First occurrence of bypass with no good explication_
12/04/2010 09:19:00 UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.

_12/11/2010 First occurrence of battery charger fault_
12/11/2010 21:35:40 UPS: A battery charger fault exists.
12/11/2010 21:35:40 UPS: Turned off for a defined period of time in response to a software command, or off while waiting for input power to return to normal.
12/11/2010 21:35:40 UPS: Turned off for a defined period of time in response to a software command, or off while waiting for input power to return to normal.

Message was edited by: iso00

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

These messages you reported indicate the PowerView was having trouble, since these are erroneous messages and do not apply to your UPS:

USF 07 Fault
External switchgear 0001 closed

Hopefully the newer v14 firmware will help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:01 AM . Last Modified: ‎2024-03-08 05:02 AM

0 Likes
0
2117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:01 AM . Last Modified: ‎2024-03-08 05:02 AM

Not sure if it actually turned off on 12/11. Haven't seen power module fault since I replaced the bad one. The charger fault and In bypass repeat independent of eachother. I did do a warmstart yesterday so i'll keep a eye on it to see if that clears it up.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:01 AM . Last Modified: ‎2024-03-08 05:02 AM

0 Likes
0
2117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:01 AM . Last Modified: ‎2024-03-08 05:02 AM

If your Symmetra is 7 years old or more, you may want to also check what firmware you have on your PowerView RM display. Current rev is 14, and 13 is known to generate false messages generally as the PowerView display itself ages.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:01 AM . Last Modified: ‎2024-03-08 05:02 AM

0 Likes
0
2117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:01 AM . Last Modified: ‎2024-03-08 05:02 AM

Where can I get the latest PowerView firmeware? All I see are the language files under downloads.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:01 AM . Last Modified: ‎2024-03-08 05:02 AM

0 Likes
0
2117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:01 AM . Last Modified: ‎2024-03-08 05:02 AM

All the available firmware is language specific. Simply download the language you want the PowerView to operate in, and that file will be the latest rev 14.

To determine your PV firmware, you can go to Display -> Info or simply unplug/replug the display and see what version it shows as it boots.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:01 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:01 AM . Last Modified: ‎2024-03-08 05:01 AM

All the available firmware is language specific. Simply download the language you want the PowerView to operate in, and that file will be the latest rev 14.

To determine your PV firmware, you can go to Display -> Info or simply unplug/replug the display and see what version it shows as it boots.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

It's on version 8 I think. Found a cable, will upgrade PowerView to latest release.

Also noticed the PowerView fault list today has the following

USF 07 Fault
External switchgear 0001 closed

Message was edited by: iso00

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

Upgraded to PowerView 14. wait and see.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

0 Likes
0
2118
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:02 AM . Last Modified: ‎2024-03-08 05:01 AM

These messages you reported indicate the PowerView was having trouble, since these are erroneous messages and do not apply to your UPS:

USF 07 Fault
External switchgear 0001 closed

Hopefully the newer v14 firmware will help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore