Unit passes self-test every 14 days, but between I see the following events in the logs. Prognosis?
01/22/2011 18:40:44 UPS: A battery charger fault no longer exists.
01/22/2011 18:40:39 UPS: A battery charger fault exists.
01/17/2011 06:40:06 UPS: No longer in bypass.
01/17/2011 06:40:02 UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.
01/16/2011 21:36:57 UPS: No longer in bypass.
01/16/2011 21:36:55 UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.
01/15/2011 15:56:56 UPS: No longer in bypass.
01/15/2011 15:56:53 UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.
01/13/2011 10:03:41 UPS: Passed a self-test.
01/13/2011 10:03:21 UPS: Started a self-test.
APP Module
Version: v3.7.2
AOS
Version: v3.7.3
Battery Capacity: 100.0 %
Runtime Remaining: 1 hour 1 minute
Nominal Battery Voltage: 120.0 VDC
Actual Battery Bus Voltage: 138.2 VDC
Last Battery Transfer: Due to software command or UPS's test control
Internal Temperature: 93.0°F
Runtime Remaining: 1 hour 2 minutes
Input Power
Input Voltage: 246.0 VAC
Input Frequency: 59.98 Hz
Output Power
Output Voltage: 211.2 VAC
Output Frequency: 59.99 Hz
Output Current: 01.3 Amps
Output Load kVA: 00.28 kVA
Output Watts at n+0: 019 %Watts
Output VA at n+0: 007 %VA
Fault Tolerance
Redundancy: n+1
Present kVA Capacity: 04.0 kVA
And a little history of events on this unit.
_12/01/2010 Batteries run down to 0% after power outage_
12/01/2010 15:13:30 UPS: A power module fault exists.
_12/02/2010 Replaced failed power module_
12/02/2010 00:59:24 UPS: A power module fault no longer exists.
_12/04/2010 First occurrence of bypass with no good explication_
12/04/2010 09:19:00 UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.
_12/11/2010 First occurrence of battery charger fault_
12/11/2010 21:35:40 UPS: A battery charger fault exists.
12/11/2010 21:35:40 UPS: Turned off for a defined period of time in response to a software command, or off while waiting for input power to return to normal.
12/11/2010 21:35:40 UPS: Turned off for a defined period of time in response to a software command, or off while waiting for input power to return to normal.
Message was edited by: iso00
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:02 AM . Last Modified: 2024-03-08 05:01 AM
These messages you reported indicate the PowerView was having trouble, since these are erroneous messages and do not apply to your UPS:
USF 07 Fault
External switchgear 0001 closed
Hopefully the newer v14 firmware will help.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:01 AM . Last Modified: 2024-03-08 05:02 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:01 AM . Last Modified: 2024-03-08 05:02 AM
Not sure if it actually turned off on 12/11. Haven't seen power module fault since I replaced the bad one. The charger fault and In bypass repeat independent of eachother. I did do a warmstart yesterday so i'll keep a eye on it to see if that clears it up.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:01 AM . Last Modified: 2024-03-08 05:02 AM
If your Symmetra is 7 years old or more, you may want to also check what firmware you have on your PowerView RM display. Current rev is 14, and 13 is known to generate false messages generally as the PowerView display itself ages.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:01 AM . Last Modified: 2024-03-08 05:02 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:01 AM . Last Modified: 2024-03-08 05:02 AM
Where can I get the latest PowerView firmeware? All I see are the language files under downloads.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:01 AM . Last Modified: 2024-03-08 05:02 AM
All the available firmware is language specific. Simply download the language you want the PowerView to operate in, and that file will be the latest rev 14.
To determine your PV firmware, you can go to Display -> Info or simply unplug/replug the display and see what version it shows as it boots.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:01 AM . Last Modified: 2024-03-08 05:01 AM
All the available firmware is language specific. Simply download the language you want the PowerView to operate in, and that file will be the latest rev 14.
To determine your PV firmware, you can go to Display -> Info or simply unplug/replug the display and see what version it shows as it boots.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:02 AM . Last Modified: 2024-03-08 05:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:02 AM . Last Modified: 2024-03-08 05:01 AM
It's on version 8 I think. Found a cable, will upgrade PowerView to latest release.
Also noticed the PowerView fault list today has the following
USF 07 Fault
External switchgear 0001 closed
Message was edited by: iso00
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:02 AM . Last Modified: 2024-03-08 05:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:02 AM . Last Modified: 2024-03-08 05:01 AM
Upgraded to PowerView 14. wait and see.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:02 AM . Last Modified: 2024-03-08 05:01 AM
These messages you reported indicate the PowerView was having trouble, since these are erroneous messages and do not apply to your UPS:
USF 07 Fault
External switchgear 0001 closed
Hopefully the newer v14 firmware will help.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.