Can't Connect to SRT2200RMXLA Via Web Console or SSH

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can't Connect to SRT2200RMXLA Via Web Console or SSH
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Gworand
Crewman Gworand
Crewman

Posted: โ€Ž2024-12-30 10:08 PM

0 Likes
5
1096
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2024-12-30 10:08 PM

Can't Connect to SRT2200RMXLA Via Web Console or SSH

As the subject indicates, I can't connect to the UPS.  I have read multiple articles and setup the IP, subnet mask, and default gateway manually for the NMC2 card using the onboard display.  I get no response to the IP address when using http or https via Chrome and SSH attempts respond with "Unable to negotiate with xxx.xxx.xxx.xxx port 22: no matching cipherfound.".  However I can ping the address and when disconnecting the ethernet cable it no longer responds.  I can also see the device using SuperScan.  From what I've read the next step is to connect using a local serial connection, but this as a hassle as it requires a USB to RJ45 adapter which isn't readily available.  Am I missing something?

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Teken
Kirk Teken
Kirk

Posted: โ€Ž2024-12-31 05:11 AM

0 Likes
4
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2024-12-31 05:11 AM

Given the limited information provided and not knowing some of the history or the facts of the entire system and network.

 

I am going to make a few assumptions that this NMC is used?!?

 

Unplug the Ethernet cable to the NMC. Take a paper clip and insert it into the reset button and hold it until you see the right side LED turn orange than release.

 

This will format the NMC and return it to a default state and enable DHCP. It will reset the user name & password to all lower case: apc

 

Insert the Ethernet cable to allow it to obtain a new IP Leased Address. Find that same address via your router, firewall, switch.

 

Go to that web address using Chrome with the user name / password: apc

 

Questions Ask . . . ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

Gworand
Crewman Gworand
Crewman

Posted: โ€Ž2025-01-01 10:48 AM

In response to Teken
0 Likes
3
1026
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-01-01 10:48 AM

Did the factory reset 3 times and got the same results via http, https, and SSH.  I can see via the menu that the IP is now set to DHCP vs static addressing.  I then retrieved the IP address (which I had already setup a reservation for) from the DNS server on my router.  Not sure what you mean by limited information provided?  I gave the UPS model number plus that it's using a NMC2 interface.  I'll provide a few more details below but please be more specific if additional info would be useful?

 

NMC2 model: AP9631

NMC2 Firmware Rev: sumx v6.8.0

UPS Firmware Rev: UPS 06.0  ID: 1010

DSP Firmware:  MCU 05.0  MBL 02.1

Comm Firmware: COM 06.0  CBL 02.1 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: โ€Ž2025-01-02 03:18 AM

In response to Gworand
0 Likes
2
1014
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-01-02 03:18 AM

The NMC needs to be updated to the latest v7.1.8 firmware. The certificate and encryption is out of date and expired.

 

If you completed the factory reset as outlined by me the system will be in a default state and both user name & password will be: apc 

 

As such use this link to download the Smart-UPS NMC firmware:

 

https://www.apc.com/us/en/product/AP9631/ups-network-management-card-2-with-environmental-monitoring...

 

Follow the wizard and prompts to upgrade the NMC. Choose FTP instead of SCP and enter user name / password of: apc 

 

Do not select backup logs . . . 

NOTE: Remove the DHCP reservation from the router. Hard boot the NMC by simply removing the card from the UPS. Wait ten seconds before inserting it back in.

 

Connect the Ethernet cable and verify the NMC shows up in the DHCP IP Leased table with a new address. Initiate the NMC firmware update following the wizard.

 

Let me know . . . 

Reply

Link copied. Please paste this link to share this article on your social media post.

Gworand
Crewman Gworand
Crewman

Posted: โ€Ž2025-01-05 12:51 AM

In response to Teken
0 Likes
0
955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-01-05 12:51 AM

Followed your instructions, downloaded the Smart UPS firmware v7.1.8 and attempted to flash using FTP.  It failed several times, so I downloaded the file a 2nd time in case there was corruption but I got the same result.  Then I pulled the card, reinserted it to force the reboot, and attempted the firmware flash again with the same result. 

 

This is getting really frustrating, I've worked in networking and have flashed firmware on many 100s of devices, so I'm not new to this type of work.  I'm trying to get this setup properly for a customer but I can't bill for all the time I'm syncing into this and it's starting to make me look bad with the customer.

 

I have located a USB to RJ45 serial adapter in case a local serial connection is the next step.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Gworand
Crewman Gworand
Crewman

Posted: โ€Ž2025-01-05 12:55 AM

In response to Teken
0 Likes
0
955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-01-05 12:55 AM

FYI, I did just try to connect to it again using Firefox.  I'm getting an "Unable to Connect" message but it is redirecting http to https, so it is providing a basic response but not granting access to the web GUI.  But it wasn't an expired cert message.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore