Can SUA5000RMT5U run properly with 240V input?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can SUA5000RMT5U run properly with 240V input?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

0 Likes
2
1978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

Can SUA5000RMT5U run properly with 240V input?

I have some SUA5000RMT5U Smart-UPS 5000VA UPSes. They have been in service ranging from one to three years. They have worked fine. I'm in the USA and the UPSes were connected to the room's 208V electrical supply.

Now somebody decides to "upgrade" the room power, and the result is that now the supply is 240V. When I plug in the UPSes, the AVR Trim alarm goes off. I have learned that some APC UPSes would let me select the output voltage (208V or 240V) but the models I have only seem to be designed to output 208V. Is this this true?

Other messages in this forum say I really should have the input and output voltages be the same, but that it won't be a disaster if the AVR Trim is on all the time. But, others say it will reduce the life expectancy of the UPSes due to extra heat generated by the transformer. Can anybody give me a definitive answer?

Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • avr
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

0 Likes
0
1978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

the SUA5000RMT5U is designed for 208v nominal input only and you're right - when fed 240v, it will constantly trim which is not recommended for any UPS. constantly trimming will cause extra heat and as you mentioned, effect the life expectancy of the UPS. more heat means the battery will most likely die earlier than it should since it would be experiencing less than ideal conditions.

the UPSs that APC offers that are allow for 208 OR 240v include the [Smart UPS RT|http://www.apc.com/products/family/index.cfm?id=163], [Symmetra RM or Symmetra LX|http://www.apc.com/products/family/index.cfm?id=189] (for single phase). these are configurable to accept either voltage and output the same voltage, meaning if you change it for a 240 input, it will output 240v to your load.

and also, yes, general practice is to have your input voltage the same as your output voltage or else you might experience issues, especially when it comes to units that have a bypass on them. when you go to bypass, utility power is fed straight through to the load. you'll see people that do it and have equipment that doesnt care, but generally it is not recommended and very well could cause damage to connected equipment.

hope that helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

0 Likes
0
1978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

Hi Doug,

SUA5000RMT5U is meant for 208V which will also provide a 208 output voltage. If you will be using the SUA5000RMT5U with 240 input voltage you might get an AVR TRIM ON(since it's sensing a high input voltage) all the time and could result for its relay to get fried.

Yes, it's true that we have units where you can select 204 or 240V output voltage. Since your room is utilizing 240V now, one of the best option for you is to use the Smart UPS RTs. You may want to check one of the part numbers that we have SURTD5000XLT. On this unit, you may configure input and output to either 208V or 240V via serial cable or thru the network management card.

I hope this helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

0 Likes
0
1979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

the SUA5000RMT5U is designed for 208v nominal input only and you're right - when fed 240v, it will constantly trim which is not recommended for any UPS. constantly trimming will cause extra heat and as you mentioned, effect the life expectancy of the UPS. more heat means the battery will most likely die earlier than it should since it would be experiencing less than ideal conditions.

the UPSs that APC offers that are allow for 208 OR 240v include the [Smart UPS RT|http://www.apc.com/products/family/index.cfm?id=163], [Symmetra RM or Symmetra LX|http://www.apc.com/products/family/index.cfm?id=189] (for single phase). these are configurable to accept either voltage and output the same voltage, meaning if you change it for a 240 input, it will output 240v to your load.

and also, yes, general practice is to have your input voltage the same as your output voltage or else you might experience issues, especially when it comes to units that have a bypass on them. when you go to bypass, utility power is fed straight through to the load. you'll see people that do it and have equipment that doesnt care, but generally it is not recommended and very well could cause damage to connected equipment.

hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore