Gracefull shutdown multiple servers, network management card question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Gracefull shutdown multiple servers, network management card question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

0 Likes
5
1980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

Gracefull shutdown multiple servers, network management card question

I have bought an SUA5000 smart UPS and is about to install it into a rack with 1 Windows, 1 Mac and 3 Linux servers. I have been researching about graceful shutdown of servers and know that I have several options: serial, USB and the network management card with PowerChute software. All servers would need to shutdown gracefully by the UPS.

I would like use the serial connection for the Windows server (as it is the one with big raid build that need the best protection) and the Network Management card/PowerCHute option to the rest of the servers.

I have a question regarding networking option: In the event of power outage, the network switches will be out as well so there will be no network service. How do the servers talk to the UPS then ? If the PowerChute is configured to look for a "loss of contact" event, how can it tell a power outage from a network traffic problem?

CAn anyone shed some light ? The Network Management Card seems to be a nice feature, but if serial connection is more reliable, then I might be prepared to buy the expansion card.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

0 Likes
0
1980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

JonPro,

While that's true, in UPSLink units (which I believe the SUA5000 is) the serial port on the UPS will still work with PowerChute even when there's a NMC in the SmartSlot. Typing twice on the serial port will bring up the NMC's configuration menus, but otherwise the serial port is speaking UPSLink.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

0 Likes
0
1980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

Thanks to voidstar and I_Picked_a_winna for your answers.

For the last bit that Pickeda_winna said, I assume it is not OK to have the a serial expander and NMC at the same time, but would it be OK to just use the built-in serial port and the NMC ? Would that set up run into communication problem as well ?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

0 Likes
0
1980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

You would have a hub (or switch) connecting your Windows, Mac, and 3 Linux servers to the Network Management Card on the UPS. That hub would also be powered by the UPS. When power goes out, the rest of the network may go down, but the UPS is still powering your hub so the local segment is still up and the NMC can command the servers to shut down.

Some folks feel more comfortable using a hardwired serial connections from the expansion card, but it's not as flexible or manageable as the NMC. Another option for you is to use a serial connection for the Windows computer and use the NMC to shut down your Mac and Linux servers.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

0 Likes
0
1980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

to add on to what voidstar mentioned, i would definitely recommend using a network management card. it will be more cost effective and has more options as far as shutdown goes. it is also supported by all of the operating systems you have and does not require additional serial cables, etc since it uses the existing network connections.

then from the network management card, you can configure email notifications, use SNMP, radius, etc. with powerchute business edition, you can do the graceful shutdown but you don't get as many bells and whistles as far as UPS monitoring features.

you also cannot use a serial interface expander and use the network management card at the same time as it is not a supported method and you will most likely run into communication problems with the UPS serial bus.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

0 Likes
0
1980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

Thudn,

Once the network management card is installed on the UPS, the serial port on it serves as the port in order for your PC to talk to the card. This method is what do we call as the local interface, it enables the user to configure the card, make some changes with the card and fix some problems which cannot be done using Web, SNMP or FTP.

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

0 Likes
0
1981
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:20 PM . Last Modified: ‎2024-03-14 02:56 AM

JonPro,

While that's true, in UPSLink units (which I believe the SUA5000 is) the serial port on the UPS will still work with PowerChute even when there's a NMC in the SmartSlot. Typing twice on the serial port will bring up the NMC's configuration menus, but otherwise the serial port is speaking UPSLink.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore