Dear Team,
Kindly let us know if we can use the undermentioned UPSs in parallel.
One ups is Galaxy300 : G3HT40KHB2S and the other is Smart-UPS VT : suvtp30kh4b4s.
If yes, what will be the accessories required to make them parallel redundant.
Thanks
Irfan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:51 AM . Last Modified: 2024-03-19 12:32 AM
Unfortunately no. For paralleling, the UPSs need to be of the same type and power rating.
SUVT and Galaxy 3500 are minor exceptions because they are named differently but ultimately the same units in most respects.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:51 AM . Last Modified: 2024-03-19 12:32 AM
Unfortunately no. For paralleling, the UPSs need to be of the same type and power rating.
SUVT and Galaxy 3500 are minor exceptions because they are named differently but ultimately the same units in most respects.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:51 AM . Last Modified: 2024-03-19 12:32 AM
Many Thanks for the detailed reply.
Rgds,
Irfan