SUVTP MBP PART NO REQUIRED UP TO FOUR UNITS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUVTP MBP PART NO REQUIRED UP TO FOUR UNITS
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

0 Likes
5
952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

SUVTP MBP PART NO REQUIRED UP TO FOUR UNITS

Dear Team,

As per below screen shot, it is confirm that the APC Smart VT can run upto Four units in parallel, we failed to find out Parallel MBP for Four units, we can find Parallel MBP for Three Units, please advise the part number of Parallel MBP which can support Four units.

This MBP is required for Smart VT 10KVA, 15KVA, 20KVA & 30KVA.40KVA

Kind Regards

Zakir

Attachments
Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

0 Likes
0
952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

here is what I can tell you from one of our 3 phase power support individuals in NAM:

SUVTOPT010 is the CAN I/O board that can be installed in the maint bypass for parallel operations. SUVTOPT009 is the parallel communications cables / box kit part of which is installed directly at each ups to be paralleled.

SBPAR30K40H-WP Is the EMEA version of the parallel capable maint bypass panel, here in NAM (especially if you

want four units in parallel), we go through the CEG team to spec out the requirements for the MBP and have it built. Due to low quantity of sales for four parallel on SUVT/G3500, we stopped carrying an active SKU and rely on CEG for those types since they as are so infrequent.

Basically SUVTOPT010 can be added to an existing system to make it parallel capable but the problem with adding after the fact is that the MBP sold with these systems is generally 1 or 2 utility inputs (dual feed). The Q1 is ups input isolation, Q3 is the maintenance bypass to tie utility directly to customer loads and Q2 is UPS output isolation. In a parallel group, you need a Q1 for each ups in the group i.e. -Q1a Q1b Q1c Q1d with four UPS's same for Q2 i.e. Q2a Q2b Q2c Q2d while Q3 only requires the 1 switch / breaker and you add a Q4 as system output isolation. This way, you can isolate individual UPS units and still provide protected power to loads or isolate entire system as necessary.

If they you wish to go with parallel systems, then I would highly recommend you go through your regular sales channels in combination with the CEG team in your region to have an appropriate three or four unit parallel capable MBP spec'd out as adding the capability after the fact allows for many errors and problems

that will be encountered. As well as with single units, MBP is not 100% necessary although always a good idea but with parallel it is very necessary

as isolating individual units can cause drop load situations and increased risk for same if no parallel MBP is used.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

0 Likes
0
952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

I think you'd want to look at the following SKUs:

SUVTOPT009 - Parallel Communication Kit

SUVTOPT010 - MBP Panel CAN I/O kit with cable

G35TOPT011 - Baying Kit

As I am based in NAM, you may need to verify with sales in your region to make sure the part numbers are the same. We were able to dig up SBPAR10K20H-WP which is a 400V panel but I hope this helps get you started in the right direction.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

0 Likes
0
952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

Thanks for the reply but the question arises, how can we configure 4 SUVT units in parallel as the below mentioned Maintenance Bypass Panels support "upto three units only"

SBPAR10K20H-WP : BYPASS PANEL for SUVT10kva-20kva UPTO THREE UNITS

SBPAR30K40H-WP : BYPASS PANEL for SUVT30kva-40kva UPTO THREE UNITS

Rgds

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

0 Likes
0
952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

Sorry about that - I guess the answer is that the SUVT / G3500 units ARE capable up to four in parallel but the tricky part is that from what I've found we do not have a standard

MBP part number for four. I believe this will require interaction with the APC Configuration Team which can happen through your regional sales team. In summary, sounds like it needs to be a special order configuration and there is no simple part number or answer to provide.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

0 Likes
0
952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

Thanks for the reply, just want to confirm the working of SUVTOPT010, and if we use till three units of SUVT in parallel and are not going for closed couple formation, can the part SUVTOPT009 and SBPAR10K20H-WP/SBPAR30K40H-WP only can make the combination (i.e without SUVTOPT010) if not, kindly help to elaborate the exact working of SUVTOPT010 in this formation, as we have installed few units of SUVT in parallel only using communication kit.

Rgds

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

0 Likes
0
953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:51 AM . Last Modified: ‎2024-03-19 12:32 AM

here is what I can tell you from one of our 3 phase power support individuals in NAM:

SUVTOPT010 is the CAN I/O board that can be installed in the maint bypass for parallel operations. SUVTOPT009 is the parallel communications cables / box kit part of which is installed directly at each ups to be paralleled.

SBPAR30K40H-WP Is the EMEA version of the parallel capable maint bypass panel, here in NAM (especially if you

want four units in parallel), we go through the CEG team to spec out the requirements for the MBP and have it built. Due to low quantity of sales for four parallel on SUVT/G3500, we stopped carrying an active SKU and rely on CEG for those types since they as are so infrequent.

Basically SUVTOPT010 can be added to an existing system to make it parallel capable but the problem with adding after the fact is that the MBP sold with these systems is generally 1 or 2 utility inputs (dual feed). The Q1 is ups input isolation, Q3 is the maintenance bypass to tie utility directly to customer loads and Q2 is UPS output isolation. In a parallel group, you need a Q1 for each ups in the group i.e. -Q1a Q1b Q1c Q1d with four UPS's same for Q2 i.e. Q2a Q2b Q2c Q2d while Q3 only requires the 1 switch / breaker and you add a Q4 as system output isolation. This way, you can isolate individual UPS units and still provide protected power to loads or isolate entire system as necessary.

If they you wish to go with parallel systems, then I would highly recommend you go through your regular sales channels in combination with the CEG team in your region to have an appropriate three or four unit parallel capable MBP spec'd out as adding the capability after the fact allows for many errors and problems

that will be encountered. As well as with single units, MBP is not 100% necessary although always a good idea but with parallel it is very necessary

as isolating individual units can cause drop load situations and increased risk for same if no parallel MBP is used.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of