Can AP9617 network mgt card be installed without interruption to UPS?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can AP9617 network mgt card be installed without interruption to UPS?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:50 PM . Last Modified: ‎2024-03-14 03:58 AM

0 Likes
4
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:50 PM . Last Modified: ‎2024-03-14 03:58 AM

Can AP9617 network mgt card be installed without interruption to UPS?

Can AP9617 network mgt card be installed without interruption to UPS?

Have like 26 APC 3000 series UPS's and need to install these cards.

Can these be "just pushed in" or does the UPS have to be turned off?

Anyone done this "hot" ?

Thanks!
C

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:50 PM . Last Modified: ‎2024-03-14 03:58 AM

0 Likes
0
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:50 PM . Last Modified: ‎2024-03-14 03:58 AM

Hi,

Sorry for the inconvenience. The knowledge base document you are referring to has been replaced with FAQ FA156597

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:50 PM . Last Modified: ‎2024-03-14 03:58 AM

0 Likes
0
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:50 PM . Last Modified: ‎2024-03-14 03:58 AM

Craig,

If you want to install the AP9617 card into the Smart UPS smart slot, then you need to completely switch off the Smart UPS before inserting or removing any SmartSlot card. Unfortunately, you can not install the NMC card without brain dead the Smart UPS.

Please view the below K-base document to know the Instructions for installing or removing a SmartSlot device with a Smart-UPS.
[http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=946]

For Matrix UPS , you need to put the Matrix into bypass by the screw on the back. Undo the screw all the way until the front display turns off. Once the display is off, the Matrix is in bypass.

For Smart-UPS RT (SURT models) you need to put the UPS in bypass using the bypass switch on the back of the unit

All Symmetra units have hot swappable SmartSlots, you do not have to alter the state of the UPS to insert and remove accessory cards.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:50 PM . Last Modified: ‎2024-03-14 03:58 AM

0 Likes
0
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:50 PM . Last Modified: ‎2024-03-14 03:58 AM

if you understand and read the above documents/information and proceed with hot swapping the cards into the UPSs, most likely the cards will not get damaged - BUT there is a slim chance they could and APC can not be liable for the damage if you don't follow the approve procedure.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:50 PM . Last Modified: ‎2024-03-14 03:58 AM

0 Likes
0
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:50 PM . Last Modified: ‎2024-03-14 03:58 AM

Why is the provided FAQ link no longer active?

If the FAQ URL has been changed, run a program to update the FAQ database.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:50 PM . Last Modified: ‎2024-03-14 03:58 AM

0 Likes
0
1168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:50 PM . Last Modified: ‎2024-03-14 03:58 AM

Hi,

Sorry for the inconvenience. The knowledge base document you are referring to has been replaced with FAQ FA156597

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of