Add power module and battery module to Symmetra LX

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Add power module and battery module to Symmetra LX
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 10:50 PM . Last Modified: โ€Ž2024-03-14 03:58 AM

0 Likes
7
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:50 PM . Last Modified: โ€Ž2024-03-14 03:58 AM

Add power module and battery module to Symmetra LX

I am going to add a power module and battery module to my Symmetra LX. This will take me from a 12kva to a 16kva and will fill up the battery slots. My question, this process is all hot swappable, right? I can just slide in my new power module and battery? I've got a SAN attached to the UPS and don't want to take a chance on it powering down.

Thanks....

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 10:50 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:50 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

So I can swap out bad moudules and batteries without having to to the UPS on BYPASS? We have an extended run cabinet connected to the mainframe and when we pulled a set of batteries out of them... it took the load down. Is there a procedure to doing hot swaps? I wish the user manual had this info.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 10:50 PM . Last Modified: โ€Ž2024-03-14 03:58 AM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:50 PM . Last Modified: โ€Ž2024-03-14 03:58 AM

I am going to add a power module and battery module to my Symmetra LX. This will take me from a 12kva to a 16kva and will fill up the battery slots. My question, this process is all hot swappable, right? I can just slide in my new power module and battery? I've got a SAN attached to the UPS and don't want to take a chance on it powering down.

Thanks....

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 10:50 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

0 Likes
0
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:50 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

So I can swap out bad moudules and batteries without having to to the UPS on BYPASS? We have an extended run cabinet connected to the mainframe and when we pulled a set of batteries out of them... it took the load down. Is there a procedure to doing hot swaps? I wish the user manual had this info.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 10:51 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:51 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

There is no procedure for hot swapping modules. You just take them out. Removing batteries would not bring your load down. The only thing that potentially could bring your load down is either removing both of the intelligence modules when the UPS is online (it needs at least one working IM installed to be online) or if you remove too many power modules, forcing the unit to switch over to bypass, but your input voltage is out of range for bypass so it drops.

The only way I could see batteries affecting your load is if the UPS is running on battery and you suddenly remove the batts, thus removing the power source.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 10:51 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:51 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

Thanks for the response... actually my customer were the ones who pulled out the batteries. And when that did they told me it took their load down. At the moment they have one bad Power Module and one bad battery on their extended run cabinet. The batteries they pulled out happen to be good batteries... they pulled out the wrong batteries may have been the cause of their load going down. Not sure??? In any case once they purchase the bad power module and battery replacing them should be a simple task! Thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 10:51 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:51 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

Yeah, who knows what customers are doing! ๐Ÿ˜‰ Hopefully they'll have better luck installing the new modules... They don't have to go to bypass, but if they feel safer that way, they can use the maintenance bypass switch to the right of the display.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 10:51 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:51 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

After their mishap I believe going on Maintain Bypass is what they will do. Thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 10:51 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:51 PM . Last Modified: โ€Ž2024-03-14 03:57 AM

as techie mentioned, you don't need to take the load down. upon inserting modules, there is nothing you need to worry about. when you are removing them, thats when you need to make sure you have adequate redundancy so that the UPS doesnt get overloaded and go to bypass. also, with the batteries, if you remove them all, you will have no battery back up.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login