We have a number of off-site locations. At each location, we have Smart-UPS 3000 and a number of devices off of each. These servers are configured to turn off after 5 minutes on battery. My question is if I run a calibration on the UPS, will this trigger this shutdown?
Thanks,
Sean
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:49 AM . Last Modified: 2024-03-08 01:56 AM
Hi Sean,
What software are you using with this? Double checking the PowerChute Business Edition Help File on this:
If UPS calibration commences and a scheduled shutdown occurs, then the operating system will shut down, but the calibration will continue and the UPS will not go to sleep.
Are you using PCBE or a network management card?
Hope this helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:49 AM . Last Modified: 2024-03-08 01:56 AM
Hi Sean,
See my post below.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:49 AM . Last Modified: 2024-03-08 01:56 AM
Hi Sean,
What software are you using with this? Double checking the PowerChute Business Edition Help File on this:
If UPS calibration commences and a scheduled shutdown occurs, then the operating system will shut down, but the calibration will continue and the UPS will not go to sleep.
Are you using PCBE or a network management card?
Hope this helps.