Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Multiple usvs
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3005:49 AM. Last Modified: 2024-03-0801:57 AM
Multiple usvs
Hi!
I have a file server that is attched to 2 USVs.
USV1 has a runtime remaining 25 minutes and USV2 has runtime remaining 13 minutes.
Low battery duration for both is 10 minutes.
when the power goes out which USV will notify the server to shutdown?
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3005:49 AM. Last Modified: 2024-03-0801:57 AM
DK,
I'm assuming you mean UPS's, not USV's.
What you would need is the Management Card (which based on your other post I am going to assume you have), installed in each UPS (So in theory, two NMC's). From there you would do a PowerChute Network Shutdown Custom Install.
When the UPS's go on battery, they will both send signals to the attached servers (if configured properly). The Servers, if they are just set to shutdown at the default low battery signal time, will wait until the SECOND UPS has signaled Low Battery Shutdown. It will ignore the first shutdown command and wait for the second.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3005:49 AM. Last Modified: 2024-03-0801:57 AM
DK,
I'm assuming you mean UPS's, not USV's.
What you would need is the Management Card (which based on your other post I am going to assume you have), installed in each UPS (So in theory, two NMC's). From there you would do a PowerChute Network Shutdown Custom Install.
When the UPS's go on battery, they will both send signals to the attached servers (if configured properly). The Servers, if they are just set to shutdown at the default low battery signal time, will wait until the SECOND UPS has signaled Low Battery Shutdown. It will ignore the first shutdown command and wait for the second.