Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
USV
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3005:48 AM. Last Modified: 2024-03-0801:57 AM
DK,
The problem you may run into is that this is not a static load. Just because you have 42 minutes remaining on battery now, does not mean that if a power demand on the UPS increases when on battery, you will have 42 minutes there.
What you would want to do is throw this into a test environment with all regularly attached equipment and watch what the NMC reports. Chances are at some point during the 11 minutes, there's going to be a fluctuation of output power by the UPS, resulting in a quick decrease in runtime, which may shutdown your Exchange server or other devices prematurely.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3005:48 AM. Last Modified: 2024-03-0801:57 AM
DK,
The problem you may run into is that this is not a static load. Just because you have 42 minutes remaining on battery now, does not mean that if a power demand on the UPS increases when on battery, you will have 42 minutes there.
What you would want to do is throw this into a test environment with all regularly attached equipment and watch what the NMC reports. Chances are at some point during the 11 minutes, there's going to be a fluctuation of output power by the UPS, resulting in a quick decrease in runtime, which may shutdown your Exchange server or other devices prematurely.