Hi!
I am not sure if I have configured my ups correctly:
Runtime is 42 minutes.
Low battery duration is 11 minutes
Shudown Delay is 180 seconds.
I have 3 servers.
Exchange which is highly critical server and needs 11 minutes to shutdown.
My file server is somewhat critical and so is my backup server. They need 5 minutes to shutdown.
Should I set PCNS on my exchange server “On Battery” shutdown after … 30 minutes ?
And the other servers default. ???
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:48 AM . Last Modified: 2024-03-08 01:57 AM
DK,
The problem you may run into is that this is not a static load. Just because you have 42 minutes remaining on battery now, does not mean that if a power demand on the UPS increases when on battery, you will have 42 minutes there.
What you would want to do is throw this into a test environment with all regularly attached equipment and watch what the NMC reports. Chances are at some point during the 11 minutes, there's going to be a fluctuation of output power by the UPS, resulting in a quick decrease in runtime, which may shutdown your Exchange server or other devices prematurely.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:48 AM . Last Modified: 2024-03-08 01:57 AM
DK,
The problem you may run into is that this is not a static load. Just because you have 42 minutes remaining on battery now, does not mean that if a power demand on the UPS increases when on battery, you will have 42 minutes there.
What you would want to do is throw this into a test environment with all regularly attached equipment and watch what the NMC reports. Chances are at some point during the 11 minutes, there's going to be a fluctuation of output power by the UPS, resulting in a quick decrease in runtime, which may shutdown your Exchange server or other devices prematurely.