Posted: 2021-06-30 07:41 PM . Last Modified: 2024-03-07 02:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:41 PM . Last Modified: 2024-03-07 02:04 AM
I'm using a SmartUPS 1000XL with battery pack.
When I try to run a calibration, it inevitably comes back as "cancelled" after a while.
The batteries are old - circa 2004. Initiating the calibration shows immediate 47% capacity remaining. Could the age of the batteries cause this problem?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:41 PM . Last Modified: 2024-03-07 02:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:41 PM . Last Modified: 2024-03-07 02:04 AM
No battery warning (but the unit is silenced as it's in a cubicle farm).
I will ask the boss to finance a couple of batteries for the unit.
(edit: I will try again with lowered sensitivity to line voltage fluctuations)
Message was edited by: Hector
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:41 PM . Last Modified: 2024-03-07 02:04 AM
The quick answer is "yes".
The batteries are not maintaining the load long enough to get a run-time calibration.
Are you not getting any battery warning?
Depending on the environment, 6 years can be a long time for batteries.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:41 PM . Last Modified: 2024-03-07 02:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:41 PM . Last Modified: 2024-03-07 02:04 AM
No battery warning (but the unit is silenced as it's in a cubicle farm).
I will ask the boss to finance a couple of batteries for the unit.
(edit: I will try again with lowered sensitivity to line voltage fluctuations)
Message was edited by: Hector