Business Edition Power Chute Questions

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Business Edition Power Chute Questions
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:38 PM . Last Modified: ‎2024-03-12 01:14 AM

0 Likes
4
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:38 PM . Last Modified: ‎2024-03-12 01:14 AM

Business Edition Power Chute Questions

I have several questions concerning the Business Edition of Power Chute.

With it installed on a lap top running Windows 10...

1. We have several different models. Will this work on all of them or are there some it won't work on? (SMT1000, SUA2200RM2U, SU1400RMXLB3U, SURTA2200RMXL2U, SMX2000RMLV2U)

2. Which cable is better to use, the serial, usb/RJ45 or USB?

3.Will one cable work for all UPS's?

4. If I plug a cable in but it doesn't see the UPS, how do I know if it's the cable, network card, or something else?

5. If all I'm wanting to do is see what kind of load is on the UPS and how long it will run when the power goes out for any number of UPS's. Is the business edition what I should be using/

6. If I can get it to work, when I plug into a UPS, will I have to reinstall the software or will it automatically see it?

7. Are there instructional videos somewhere that could show me how to run the software so I can make sure I've installed it correctly?

Thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:38 PM . Last Modified: ‎2024-03-12 01:14 AM

0 Likes
0
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:38 PM . Last Modified: ‎2024-03-12 01:14 AM

Hi,

On 8/31/2017 3:11 PM, bob said:

1. We have several different models. Will this work on all of them or are there some it won't work on? (SMT1000, SUA2200RM2U, SU1400RMXLB3U, SURTA2200RMXL2U, SMX2000RMLV2U)

Yes and no. PowerChute Business Edition is compatible with all of those Smart-UPS but you need different versions depending on the model. SMT, SMX will communicate with PowerChute Business Edition version 9.2. SU, SUA, SURTA models will communicate with version 9.0.3. Both version are included in the installer and when the installer is run it determines the proper version base on the connected UPS. Example, if you attach SMT1000 when the installer is run version 9.2 will be installed. If you then connect the SUA2200RM2U the UPS will not be discovered. You will need to uninstall version 9.2 and install 9.0.3. 

On 8/31/2017 3:11 PM, bob said:

2. Which cable is better to use, the serial, usb/RJ45 or USB?

Depends on the model. SU1400RMXL is serial only comm while the other support both serial and USB. 

On 8/31/2017 3:11 PM, bob said:

3.Will one cable work for all UPS's?

No.

On 8/31/2017 3:11 PM, bob said:

4. If I plug a cable in but it doesn't see the UPS, how do I know if it's the cable, network card, or something else?

Difficult to say since all of the Smart-UPS are different. 

On 8/31/2017 3:11 PM, bob said:

5. If all I'm wanting to do is see what kind of load is on the UPS and how long it will run when the power goes out for any number of UPS's. Is the business edition what I should be using/

Business Edition will provide that information but remember you need the Business Edition Agent communicating with the UPS and the Agent can only communicate with a single UPS at a time. 

On 8/31/2017 3:11 PM, bob said:

6. If I can get it to work, when I plug into a UPS, will I have to reinstall the software or will it automatically see it?

If you are switching between compatible UPS you should stop the PowerChute Service then connect to the UPS and restart the Service. If the UPS is not compatible with the installed version then comm will not be established and describe in answer to #1

On 8/31/2017 3:11 PM, bob said:

7. Are there instructional videos somewhere that could show me how to run the software so I can make sure I've installed it correctly?

Yes. SChneider Electric FAQ FA249054

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:38 PM . Last Modified: ‎2024-03-12 01:14 AM

0 Likes
0
1067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:38 PM . Last Modified: ‎2024-03-12 01:14 AM

Hi,

On 8/31/2017 3:11 PM, bob said:

1. We have several different models. Will this work on all of them or are there some it won't work on? (SMT1000, SUA2200RM2U, SU1400RMXLB3U, SURTA2200RMXL2U, SMX2000RMLV2U)

Yes and no. PowerChute Business Edition is compatible with all of those Smart-UPS but you need different versions depending on the model. SMT, SMX will communicate with PowerChute Business Edition version 9.2. SU, SUA, SURTA models will communicate with version 9.0.3. Both version are included in the installer and when the installer is run it determines the proper version base on the connected UPS. Example, if you attach SMT1000 when the installer is run version 9.2 will be installed. If you then connect the SUA2200RM2U the UPS will not be discovered. You will need to uninstall version 9.2 and install 9.0.3. 

On 8/31/2017 3:11 PM, bob said:

2. Which cable is better to use, the serial, usb/RJ45 or USB?

Depends on the model. SU1400RMXL is serial only comm while the other support both serial and USB. 

On 8/31/2017 3:11 PM, bob said:

3.Will one cable work for all UPS's?

No.

On 8/31/2017 3:11 PM, bob said:

4. If I plug a cable in but it doesn't see the UPS, how do I know if it's the cable, network card, or something else?

Difficult to say since all of the Smart-UPS are different. 

On 8/31/2017 3:11 PM, bob said:

5. If all I'm wanting to do is see what kind of load is on the UPS and how long it will run when the power goes out for any number of UPS's. Is the business edition what I should be using/

Business Edition will provide that information but remember you need the Business Edition Agent communicating with the UPS and the Agent can only communicate with a single UPS at a time. 

On 8/31/2017 3:11 PM, bob said:

6. If I can get it to work, when I plug into a UPS, will I have to reinstall the software or will it automatically see it?

If you are switching between compatible UPS you should stop the PowerChute Service then connect to the UPS and restart the Service. If the UPS is not compatible with the installed version then comm will not be established and describe in answer to #1

On 8/31/2017 3:11 PM, bob said:

7. Are there instructional videos somewhere that could show me how to run the software so I can make sure I've installed it correctly?

Yes. SChneider Electric FAQ FA249054

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:38 PM . Last Modified: ‎2024-03-12 01:14 AM

0 Likes
0
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:38 PM . Last Modified: ‎2024-03-12 01:14 AM

This is perfect. Thank you so much. I'm also thinking that I will need to install not only with each different UPS but if I'm on a different network as well.

Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:38 PM . Last Modified: ‎2024-03-12 01:14 AM

0 Likes
0
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:38 PM . Last Modified: ‎2024-03-12 01:14 AM

Is there a list of UPSs that a particular version will work with or do I just try it and if it doesn't see it, uninstall the version I have a reinstall the program again?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:38 PM . Last Modified: ‎2024-03-12 01:13 AM

0 Likes
0
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:38 PM . Last Modified: ‎2024-03-12 01:13 AM

Hi,

SMT, SMX, SRT, SMC, and SURTD model Smart-UPS use PowerChute Business Edition 9.2. Any other Smart-UPS will use version 9.0.3.

BTW: There is versions 9.2.1 and 9.0.4 available attached to this FAQ FA304446 These versions have an updated version of java. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore