Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Brand new Symmetra LX - On bypass due to fault

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Brand new Symmetra LX - On bypass due to fault
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
APC Symmetra LX 16kVA Scalable to 16kVA N+1 Rack-mount, 208/240V

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2021-10-13 03:57 AM . Last Modified: ‎2021-10-13 04:01 AM

0 Likes
2
2733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-13 03:57 AM . Last Modified: ‎2021-10-13 04:01 AM

Brand new Symmetra LX - On bypass due to fault

Hi,

 

Hopefully someone can help us with this.  We have just had a brand new Symmetra LX 16000 RM installed.  A few weeks later, we were getting lots of alerts:

 

09/25/2021    05:46:18    Device    UPS: The main intelligence module is now in control.    0x0220
09/25/2021    05:46:10    Device    UPS: A main intelligence module fault no longer exists.    0x0204
09/25/2021    05:45:50    Device    UPS: A main intelligence module fault exists.    0x0203
09/25/2021    05:45:49    Device    UPS: A main intelligence module fault no longer exists.    0x0204
09/25/2021    05:45:24    Device    UPS: A main intelligence module fault exists.    0x0203
09/25/2021    05:45:23    Device    UPS: Redundant Intelligence Module In Control    0x021F

 

AND

 

09/26/2021    17:45:54    Device    UPS: The number of batteries decreased.    0x0242
09/25/2021    05:46:33    Device    UPS: The number of batteries increased.    0x0241
09/25/2021    05:46:18    Device    UPS: The number of batteries decreased.    0x0242

 

APC suggested that we remove and reinsert the MIM.  We duly put it into logical and maintenance bypass and I removed and reinserted the MIM, then after 30 seconds and with the MIM status green as expected, removed and reinserted the RIM (just in case that was the issue, didn't want to do this twice).  The UPS then stated "UPS in bypass due to a fault".  Neither display or web access give any further clues as to the fault, everything shows as normal including power modules, MIM, RIM, batteries, etc..

 

That was last Thursday evening, so far APC have asked for some information and otherwise done nothing (despite desparate pleas for an update).  We have been stuck in maintenance bypass with no backup or under/overvoltage protection for nearly a week!

 

I suspect it's got confused and that a reboot of the UPS electronics will fix it.  As far as I can see, I can cycle the System Enable switch whilst in maintenance bypass without dropping the load?

 

Alternatively, maybe a self-test will force it to discover that there is no fault after all.  But again, I don't want to do anything to drop the load.

 

Suggestions very welcome!

 

 

Regards,

 

Sid

First time Symmetra user, currently wishes he stayed with multiple SmartUPS units 😞

Labels
  • Labels:
  • Datacenter UPS
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
APC_Matt
Lieutenant JG APC_Matt Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-14 05:29 AM

0 Likes
0
2717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-14 05:29 AM

Hi Sid

 

I'm working with the UK customer care team to resolve this with you.

 

Matt

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-10-22 03:13 AM

0 Likes
0
2671
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-22 03:13 AM

14 days have now passed since our new Symmetra got stuck on bypass due to a fault.  After 14 days with no working UPS, we have still not received any useful suggestions from APC.  In some instances, 48 hours have passed without any updates.  Even the installer (a major UK data centre provider) was unable to get any useful suggestions from APC technical support.

 

Faced with another weekend with no working UPS, I took the matter into my own hands and started experimenting.  For the sake of any other Symmetra LX customers, here is how I resolved the faults "On bypass due to a fault" and "Fault, Power Module Will Not Turn Off":

 

  1. Due to the issues listed in the original post, APC instructed us to reseat the Main Intelligence module.  It since turns out that these issues are a known firmware fault (not due to be fixed until December 2021)!
  2. Reseating the MIM result in the UPS in maintenance bypass and reporting "On bypass due to a fault".  
  3. After FOURTEEN days of waiting for APC to suggest something useful, we turned off the System Enable switch with the intention of restart the UPS.  After 30 seconds, turned on the System Enable switch.
  4. UPS started up and reported "Fault, Power Module Will Not Turn Off".  Googling this message brought no answers.  No individual power modules listed as being at fault.
  5. Checked all diagnostic information including raw status information.  All power modules, batteries, XR modules and intelligence modules showing no faults.
  6. Removed and re-seated the Main Intelligence Module.  When it took back control from the Redundant Intelligence module, the fault disappeared and the fault light was extinguished.
  7. Released maintenance bypass and logical bypass and the UPS is back running again.

 

My happiness in having a working UPS is balanced by the frustration and disappointment that we had to resort to workout out the solution ourselves.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore