My office is in "70-volt" brownout. The APC's correctly did graceful shutdown. The 70 volts iss enough so that all batteries are now at 100%.
I want to boot a server from the APC (SmartUPS1500) and run it for about 10 minutes. Then do another graceful shutdown so everything is set to automatically come back online when power outage ends.
Can I force the APC to power on? I don't see any documentation about this.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:32 AM . Last Modified: 2024-03-15 04:58 AM
Hi,
You can cold start the Smart-UPS. Unplug the UPS from the AC source, press the power-on button. The UPS will start on battery power.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:32 AM . Last Modified: 2024-03-15 04:58 AM
Hi,
You can cold start the Smart-UPS. Unplug the UPS from the AC source, press the power-on button. The UPS will start on battery power.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.