What happens to the expected 3 to 5 year battery lifetime for a replacement battery (e.g. RBC43) if it is not charged every 3 to 6 months while in storage?
What is the effect of not ever charging it to 100% within 6 months of purchase as recommended?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:18 AM . Last Modified: 2024-03-19 03:01 AM
What would be nice is a dedicated charger that you can plug a single battery cartridge into.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:18 AM . Last Modified: 2024-03-19 03:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:18 AM . Last Modified: 2024-03-19 03:01 AM
I continued to research these questions in your FAQs and discovered the following:
FA157446 | 8.0 |
...
Allowing batteries to stand for long time after a discharge without recharging will cause plate"sulfation." Sulfation is the formation of large crystals or hard lead sulfate on the battery plates.Excessive sulfation of this kind is difficult to reduce and may cause premature damage (i.e.overheating or inability of the battery to retain charge). Lead sulfate is difficult and some times impossible to reduce by conventional charging methods.
...
A discharged battery needs to be recharged within 72 hours of the discharge to avoid permanent battery damage.
...
Does anyone have any comments that significantly change the conclusion that once the batteries are discharged beyond the "sulfation" limit that they are degraded to the point that they need to be replaced?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:18 AM . Last Modified: 2024-03-19 03:01 AM
Don't know if these help: http://www.apc.com/prod_docs/results.cfm?DocType=White+Paper&query_type=99&keyword=vrla
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:18 AM . Last Modified: 2024-03-19 03:01 AM
What would be nice is a dedicated charger that you can plug a single battery cartridge into.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.