Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Battery options for 2200 (model: SUA2200UXI)
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3010:53 PM. Last Modified: 2024-03-0610:33 PM
I have actual experience using a SUA3000RM2U with TWO battery banks of 4-155 AH batteries each, for over 8 hours continuously. This set up for emergency power only and requires close monitoring of both the UPS (NMC) and batteries (actual voltage and/or specific gravity). The charging circuit of the UPS is not designed to recharge such a large bank of batteries and the UPS "smarts" will lose track of the battery charge conditions. This will require that you ignore alarms and to also have an alternate method of charging the batteries.
IMO, these are amazingly robust units and can be utilized with larger battery systems. However, for use in the services that they were intended (backup power for sensitive electronics), you should use extended run units with properly designed added battery packs and the UPS itself properly configured for the actual number of added battery packs. This will allow you to confidently leave the system unattended for it's intended purpose.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3010:53 PM. Last Modified: 2024-03-0610:33 PM
I have actual experience using a SUA3000RM2U with TWO battery banks of 4-155 AH batteries each, for over 8 hours continuously. This set up for emergency power only and requires close monitoring of both the UPS (NMC) and batteries (actual voltage and/or specific gravity). The charging circuit of the UPS is not designed to recharge such a large bank of batteries and the UPS "smarts" will lose track of the battery charge conditions. This will require that you ignore alarms and to also have an alternate method of charging the batteries.
IMO, these are amazingly robust units and can be utilized with larger battery systems. However, for use in the services that they were intended (backup power for sensitive electronics), you should use extended run units with properly designed added battery packs and the UPS itself properly configured for the actual number of added battery packs. This will allow you to confidently leave the system unattended for it's intended purpose.