Battery Power is too low to support the load : Smart UPS 3000VA RM

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Battery Power is too low to support the load : Smart UPS 3000VA RM
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:27 AM

0 Likes
4
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:27 AM

Battery Power is too low to support the load : Smart UPS 3000VA RM

Dear All,

I have a SmartUPS 3KVA RM feeding our servers. The network management interface shows that the load is 39% and the battery cpapcity is 100%. When I power up a new box which I just connceted to the UPS the following happens and the NMI initiates a shutdown:

"08.01.2009 17:35:08 UPS: A discharged battery condition no longer exists.
08.01.2009 17:34:44 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately."

I could see the battery indictor on the UPS flashing green (no it does not turn yellow) the momemnt I power up the new box. I got "UPS: A discharged battery condition no longer exists" once I powered down the new box, before the NMI/UPS initiates a shutdown.

The battery is fairly new battery which was installed in last October.

I first thought that batteries are not getting charged for some reason, but then I sould not see a100% battery capacity, should I?

Thank you for your help.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

Hello jgreco,

Sheduled a service interruption to inspect the battery pack yesterday. The batteies carried a data stamp of 0031022, which I interpreted as made in 2003, since this UPS has been bought in mid 2004 (in Australia). Then I found out that it was the NMC which had been replaced last year not the battery pack!

I have two queries:
1. As you correctly thought it is the old style 3000VA RM. I just looked up one of our supplier wbsite for the replacement battery pack. Is RBC#43 the correct replacement for this? Connections in RBC#12 seems to be a bit different from (going by the picture there) what we have. Or can I just buy RBC#12 for me to re-wire the 4 batteries into the enclosure? - is there any warranty complication with this approach?
2. What is the best way to re-calibrate the UPS once a new battery pack is installed? If it is with a calibration key, how can I get one? Have you got to order one from APC AUS or does it come along with a battery pack?

Thanks for your help.

Regards

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:27 AM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:27 AM

Hi:

What does the remaining runtime indicate on your NMC? Also, what is your "Low Battery Duration" setting set to? You can find this setting either under Smart-UPS - Configuration, or under UPS - Shutdown (depending on the firmware rev). When you replaced this battery, did you replace it with an APC RBC?

It sounds like either that setting may be too high, or the runtime may be read inaccurately and may need to be re-calibrated.

Let me know and we can help you resolve this.

Thanks,E

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:27 AM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:27 AM

Hello CMFR,

Thank you kindly for you post.
1. UPS/NMC settings:
"Low Battery Duration" set to 02 minutes and "Shutdown Delay" set to 90sec
2. "Remaining Runtim" showing is 6 minutes
3. Yes, the replacement battery was a APC replacement battery.

Thanks and Reagrds

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:26 AM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:26 AM

39% load and the runtime's 6 minutes, on new batteries? Something's wrong.

I looked around and found a SU3000RM here with 36.4% load, batteries about two years old, and it's estimating 18 minutes run. Yours ought to be 20 or more, IMHO.

The "recalibrate" suggestion is good, of course. However, usually I've found other things to be wrong. Note that if you recalibrate and something's wrong, you might find your load dropped, etc.

If you have the older, non-2U variant of the RM, one of the most common things that causes problems like this is someone managing to knock off a battery wire while installing the batteries. From time to time, we find a connector that's not quite as tight as it might be. If you lose a wire, the RBC will appear to continue to work, because it is a pack that has two batteries in series, and two sets in parallel. You go down to one set in parallel, and suddenly your 3000VA UPS becomes something more like a gimped 1500VA. That looks vaguely like your symptom.

The other thing to consider is the source you used for the RBC. Sadly, SLA batteries have a relatively short shelf life. I know that many companies like to shop for batteries based on price, but in the case of something like the RBC12, you don't necessarily have a lot of people buying them, and are you sure it hasn't been sitting on a shelf for six months? The end result will be batteries that severely underperform. The battery pack of an RBC12 is, of course, the same as the battery pack for the RBC8, just without the fuse wiring. This always annoyed me a little bit, from an end-user point of view, it'd be easier to guarantee freshness of your RBC if there weren't as many models.

You might want to see if you can identify a datecode on the batteries. For example, Yuasa/EnerSys Genesis batteries typically are marked xYMMDD, and if the batteries were more than maybe nine months old when you bought them, that's going to have a negative impact.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

Hello jgreco,

Sheduled a service interruption to inspect the battery pack yesterday. The batteies carried a data stamp of 0031022, which I interpreted as made in 2003, since this UPS has been bought in mid 2004 (in Australia). Then I found out that it was the NMC which had been replaced last year not the battery pack!

I have two queries:
1. As you correctly thought it is the old style 3000VA RM. I just looked up one of our supplier wbsite for the replacement battery pack. Is RBC#43 the correct replacement for this? Connections in RBC#12 seems to be a bit different from (going by the picture there) what we have. Or can I just buy RBC#12 for me to re-wire the 4 batteries into the enclosure? - is there any warranty complication with this approach?
2. What is the best way to re-calibrate the UPS once a new battery pack is installed? If it is with a calibration key, how can I get one? Have you got to order one from APC AUS or does it come along with a battery pack?

Thanks for your help.

Regards

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of