Adjust charging one 2200 XLs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Adjust charging one 2200 XLs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

0 Likes
8
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

Adjust charging one 2200 XLs

Is there way to adjust the charging on a 2200 Xls?
Ours seems to be continually overcharging the batteries.
What is the normal voltage range on fully charged batteries for this unit?

Thank you

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

0 Likes
0
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

Thank you so much for your time and effort in posting. Now I realize this is getting deeply proprietary, but, I have seen people on the forums use what has been coined the APC Smart Protocol to adjust the voltage gain and reduce the output voltage using a dumb terminal interface, this may be what you're referring to. This has been reported to work better on some units more than others. It has been reported on the 1500 series to reduce float voltage but on the 2200, it only changes the reported voltage. I have also read that people replace the charging capacitor that usually goes out, and, I wouldnt mind replacing this.

I am a skilled and adept engineer, so changing capacitors and reprogramming is not something I have any qualms about and realise all the issues regarding "at my own risk" and if it gives me another year before I trade up, it would be worth it.

As far as operations, it is not working correctly and I can only presume this is, again, a voltage calibration issue, it reports a variable run time, now it reports 11% load and 14minutes of run time. It should be over 45 -60 minutes of run time at this load level, which tells me it is not calibrated properly.

Michael

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

Thank you

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

There is no way to change the charging operation of the batteries. What voltages are you seeing? The nominal voltage is usually a bit lower than the average float voltage (which is generally about 54/55v for float and what youll actually see.). This is normal.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

We are seeing 54.8 volts.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

ok so that is perfectly fine. as mentioned already, this is the correct float voltage for the 48v battery in this UPS.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

We are seeing 55.9 volts at the battery terminals and also as indicated in battery status, what should we do??

Michael

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

from the various threads on the forum you have posted on, it appears your unit is very old. since then, battery management has been severely improved on those types of UPSs to avoid issues like this.

i cant find the thread on it now but i thought there was one a while ago about what to adjust in the UPS that you could do at your own risk. i will see if i can find it.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

cant find it! maybe i am thinking of something else.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:10 PM . Last Modified: ‎2024-03-15 01:26 AM

Thank you so much for your time and effort in posting. Now I realize this is getting deeply proprietary, but, I have seen people on the forums use what has been coined the APC Smart Protocol to adjust the voltage gain and reduce the output voltage using a dumb terminal interface, this may be what you're referring to. This has been reported to work better on some units more than others. It has been reported on the 1500 series to reduce float voltage but on the 2200, it only changes the reported voltage. I have also read that people replace the charging capacitor that usually goes out, and, I wouldnt mind replacing this.

I am a skilled and adept engineer, so changing capacitors and reprogramming is not something I have any qualms about and realise all the issues regarding "at my own risk" and if it gives me another year before I trade up, it would be worth it.

As far as operations, it is not working correctly and I can only presume this is, again, a voltage calibration issue, it reports a variable run time, now it reports 11% load and 14minutes of run time. It should be over 45 -60 minutes of run time at this load level, which tells me it is not calibrated properly.

Michael

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of