couple questions. Just got my 3000XL.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • couple questions. Just got my 3000XL.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
134
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:27 AM

0 Likes
1
546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:27 AM

couple questions. Just got my 3000XL.

I was reading the forum and I read about some guy whose Dell switches off when he loses power and the UPS is switching to battery. I have 3 Dell poweredge servers with dual power supplies. I have a 1950, a 2950, and a 2900. The 2900 runs iscsi so that thread made me a little nervous. A few weeks ago 3 of my servers turned off when the AC in the server room turned on. The lights flashed on and off for a split-second and some servers turned off and others stayed on. The 2900 that is filled with SAS disks running iSCSI for all my virtual machines was one of the servers that went off.

My question is, does it make any difference whether I use a Y-cord to plug both PSUs into the same socket on the UPS? Or should I use 2 separate power cords? Similarly, is there a down side to running a power bar from one of the UPS sockets?

Third, I'm designing the new cable layout for the server room (investing in some cable management to get it under control). I as of yet do not have my 30 amp circuit installed for the UPS. It's like 3 weeks behind schedule because the building is waiting on a part so I can't get in to configure PowerChute yet. I'm wondering if i can shut down individual sockets and leave others up to maximize battery when the power goes out? On the same note, if i use separate sockets for the servers with dual power supplies, i could shut one of them down early and save some battery...

Thanks.

Message was edited by: jrs91

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:27 AM

0 Likes
0
546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:27 AM

hi

to begin, do you have an SUA3000XL or an SUM3000RMXL3U?

i am going to assume that it is an SUA3000XL at this point.

My question is, does it make any difference whether I use a Y-cord to plug both PSUs into the same socket on the UPS? Or should I use 2 separate power cords?
The only thing you need to worry about is not overloading the UPS/outlets and their respective circuit breakers per the labels on the back. Just a note which I think you already know - I mean plugging the redundant PSUs into the same UPS isnt 100% redundant in a power outage but of course it is if the actual hardware fails and the PSU craps out.
Similarly, is there a down side to running a power bar from one of the UPS sockets?
You can do this as well but still need to be aware of the UPS VA/Watt rating as well as the outlet and breaker ratings of the particular banks on the UPS. Also, make sure you use a [power distribution unit|http://www.apc.com/products/category.cfm?id=6&subid=48] rather than a random "power bar" or surge protector type of thing since the PDUs distribute power evently, etc


Third, I'm designing the new cable layout for the server room (investing in some cable management to get it under control). I as of yet do not have my 30 amp circuit installed for the UPS. It's like 3 weeks behind schedule because the building is waiting on a part so I can't get in to configure PowerChute yet. I'm wondering if i can shut down individual sockets and leave others up to maximize battery when the power goes out? On the same note, if i use separate sockets for the servers with dual power supplies, i could shut one of them down early and save some battery...
On the SUA3000XL, there is no functionality to shutdown individual outlets on the UPS itself. You can only do this on a Switched Rack PDU which is visible on the link for the Power Distribution units above. You are able to log into the PDU itself, aside from the UPS, and control individual outlets. If you randomly have the SUM3000RMXL3U UPS, this unit comes with outlet banks which you CAN individually power off and load shed through the network management card that ships with it.

let us know if you have any other questions! hope this helps!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:27 AM

0 Likes
0
547
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:09 PM . Last Modified: ‎2024-03-15 01:27 AM

hi

to begin, do you have an SUA3000XL or an SUM3000RMXL3U?

i am going to assume that it is an SUA3000XL at this point.

My question is, does it make any difference whether I use a Y-cord to plug both PSUs into the same socket on the UPS? Or should I use 2 separate power cords?
The only thing you need to worry about is not overloading the UPS/outlets and their respective circuit breakers per the labels on the back. Just a note which I think you already know - I mean plugging the redundant PSUs into the same UPS isnt 100% redundant in a power outage but of course it is if the actual hardware fails and the PSU craps out.
Similarly, is there a down side to running a power bar from one of the UPS sockets?
You can do this as well but still need to be aware of the UPS VA/Watt rating as well as the outlet and breaker ratings of the particular banks on the UPS. Also, make sure you use a [power distribution unit|http://www.apc.com/products/category.cfm?id=6&subid=48] rather than a random "power bar" or surge protector type of thing since the PDUs distribute power evently, etc


Third, I'm designing the new cable layout for the server room (investing in some cable management to get it under control). I as of yet do not have my 30 amp circuit installed for the UPS. It's like 3 weeks behind schedule because the building is waiting on a part so I can't get in to configure PowerChute yet. I'm wondering if i can shut down individual sockets and leave others up to maximize battery when the power goes out? On the same note, if i use separate sockets for the servers with dual power supplies, i could shut one of them down early and save some battery...
On the SUA3000XL, there is no functionality to shutdown individual outlets on the UPS itself. You can only do this on a Switched Rack PDU which is visible on the link for the Power Distribution units above. You are able to log into the PDU itself, aside from the UPS, and control individual outlets. If you randomly have the SUM3000RMXL3U UPS, this unit comes with outlet banks which you CAN individually power off and load shed through the network management card that ships with it.

let us know if you have any other questions! hope this helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore