This is a SmartUPS 3000 RM.
The red replace battery indicator was light.
I replaced the battery with a new battery from APC.
The load is 2/5 and the 2 Load LEDs are on continuously.
The 5 Battery Charge LEDs are flashing continuously.
The User Manual
http://excessups.com/manuals/APC_SUA3000RMXL3U_users_manual.pdf
doesn't indicate what the problem is when just the Battery Charge
LEDs are flashing.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:52 AM . Last Modified: 2024-03-12 11:06 PM
This is explained in our knowledge base -> http://www.apc.com/support/index?page=content&country=US〈=en&id=FA156538
This usually means low runtime based on what you've said. You should probably pursue doing a runtime calibration as noted in the article to update the runtime.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:52 AM . Last Modified: 2024-03-12 11:06 PM
This is explained in our knowledge base -> http://www.apc.com/support/index?page=content&country=US〈=en&id=FA156538
This usually means low runtime based on what you've said. You should probably pursue doing a runtime calibration as noted in the article to update the runtime.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.