Batteries status: Not Installed

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Batteries status: Not Installed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 02:27 AM . Last Modified: ‎2024-03-05 11:21 PM

0 Likes
3
1395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:27 AM . Last Modified: ‎2024-03-05 11:21 PM

Batteries status: Not Installed

Hi.

A few days back, I was having troubles with my LX 1600 UPS. I had a couple of batteries in low capacity status. A few days after that I tried to replace the old batteries with new ones and it was useless. The UPS says me that the new batteries, and the old ones not  replaced yet, have an  Status of Not Installed.

Please, if anyone knows how to fix this, let know.

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:27 AM . Last Modified: ‎2024-03-05 11:21 PM

0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:27 AM . Last Modified: ‎2024-03-05 11:21 PM

The only other thing you might need to do is turn the batteries on. They come turned off to prevent discharge when in storage. If you look at the front of the SYBT5 module, there is a black knob. See image here for what I am talking about -> SYBT5 - More Images

You'll need to make sure that is in the ON position which I believe is would be vertical. This is easy to do with a coin or similar to facilitate turning the knob.

1087_IMAGE%2430A940F581831B18.jpg

This assumes you're inserting them directly into the Symmetra LX UPS battery bays. If you have any external run frames, the battery orientation/position is different so you can't always go by this positioning. In an XR frame, the batteries are rotated counter clockwise 90º on their side in their bays so "9 o clock" would be ON and "12 o clock" for OFF.

If this does not work, try turning off the battery again and back on. sometimes the switch does not catch to turn them on. If you're sure they are ON, you can try different bays if you do have batteries that work properly to verify there is not an issue with the particular bay.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:27 AM . Last Modified: ‎2024-03-05 11:21 PM

0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:27 AM . Last Modified: ‎2024-03-05 11:21 PM

What batteries did you replace? The Symmetra LX system has intelligence batteries and the entire SYBT5 module needs to be replaced. You should not be replacing the (10) 12vDC batteries within the module as the intelligence inside that module will not recognize that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:27 AM . Last Modified: ‎2024-03-05 11:21 PM

0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:27 AM . Last Modified: ‎2024-03-05 11:21 PM

Hello Angela.

I replaced the hole SYBT5 module. I didn't open the module and replaced some batteries.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:27 AM . Last Modified: ‎2024-03-05 11:21 PM

0 Likes
0
1397
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:27 AM . Last Modified: ‎2024-03-05 11:21 PM

The only other thing you might need to do is turn the batteries on. They come turned off to prevent discharge when in storage. If you look at the front of the SYBT5 module, there is a black knob. See image here for what I am talking about -> SYBT5 - More Images

You'll need to make sure that is in the ON position which I believe is would be vertical. This is easy to do with a coin or similar to facilitate turning the knob.

1087_IMAGE%2430A940F581831B18.jpg

This assumes you're inserting them directly into the Symmetra LX UPS battery bays. If you have any external run frames, the battery orientation/position is different so you can't always go by this positioning. In an XR frame, the batteries are rotated counter clockwise 90º on their side in their bays so "9 o clock" would be ON and "12 o clock" for OFF.

If this does not work, try turning off the battery again and back on. sometimes the switch does not catch to turn them on. If you're sure they are ON, you can try different bays if you do have batteries that work properly to verify there is not an issue with the particular bay.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore