Batteries hot swapable and power cycle during sellf-test

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Batteries hot swapable and power cycle during sellf-test
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:49 AM . Last Modified: ‎2024-03-15 05:47 AM

0 Likes
3
1051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:49 AM . Last Modified: ‎2024-03-15 05:47 AM

Batteries hot swapable and power cycle during sellf-test

Hi,

2 questions for you.

1. I have a SMT2200RM2U Smart UPS. It performed a scheduled self test last night and it caused the closet switches to lose power/power cycle. I manually performed a self test again with the same result. It is my understanding that the self test should not cause a power outage for connected devices. Is this correct? If so, then I believe I have a faulty battery.

2. Are the batteries in my UPS hot swappable with zero downtime?

 

Thanks

 

Jeremy

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 2200
  • apc
  • battery
  • fault
  • smart-ups
  • smartups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:49 AM . Last Modified: ‎2024-03-15 05:47 AM

0 Likes
0
1052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:49 AM . Last Modified: ‎2024-03-15 05:47 AM

Hi Jeremy  - 

SMT units will generally not drop the load during a self test, but it can happen on occasion with severely depleted batteries. Typically you would see this in applications where there is no remote monitoring and no one heard the unit beeping when the replace battery alert initially happened. Given your serial number your UPS is just over 6 years of age. Batteries typically last 3-5 years, so assuming it still has the original batteries, this would make sense. The best way to ensure that a load does not drop due to bad batteries is to ensure that batteries are replaced promptly as soon as the UPS indicates that they are bad. Another possible factor is the physical environment - Overly warm environments can cause batteries to fail quickly rather than giving you a few weeks notice. Batteries will perform best in an environment that is 68-77F. If your room is consistently warmer than that, you may not experience optimal battery performance.

Thanks,

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:49 AM . Last Modified: ‎2024-03-15 05:47 AM

0 Likes
0
1052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:49 AM . Last Modified: ‎2024-03-15 05:47 AM

Hi Jeremy,

Can you please provide the serial number for this unit. This will help determine how old the product is and whether it is in fact behaving as designed.

The unit uses the RBC43 battery.

The following come from an FAQ found on the APC.com website.

Since our introduction of user replaceable batteries in 1995, all Smart-UPS products have featured hot swap battery modules. This means you can safely remove and replace your battery module without affecting your load. It is important to remember that during the brief time that your battery is disconnected, you will have no battery back up available should a power event occur. Because of this we advise that you never hot swap a battery when your power is unstable. If you are experiencing severe weather conditions or your UPS is frequently switching to battery/regulating voltage, we recommend you wait until conditions stabilize. 

Once your battery is replaced you should allow it to charge to 100%, then run a self test:  

  • Legacy Products (No LCD Display) - Press and hold the "I/Test" button. Let go once the UPS switches to battery.
  • Next Generation Products (LCD Screen) - Go to the "Test and Diagnostics" menu, then select "Start UPS Self Test"

When the self test is complete the Replace Battery Indicator should turn off. 

SecretSquirrel

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:49 AM . Last Modified: ‎2024-03-15 05:47 AM

0 Likes
0
1053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:49 AM . Last Modified: ‎2024-03-15 05:47 AM

The serial number of my unit is AS1350242762

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:49 AM . Last Modified: ‎2024-03-15 05:47 AM

0 Likes
0
1053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:49 AM . Last Modified: ‎2024-03-15 05:47 AM

Hi Jeremy  - 

SMT units will generally not drop the load during a self test, but it can happen on occasion with severely depleted batteries. Typically you would see this in applications where there is no remote monitoring and no one heard the unit beeping when the replace battery alert initially happened. Given your serial number your UPS is just over 6 years of age. Batteries typically last 3-5 years, so assuming it still has the original batteries, this would make sense. The best way to ensure that a load does not drop due to bad batteries is to ensure that batteries are replaced promptly as soon as the UPS indicates that they are bad. Another possible factor is the physical environment - Overly warm environments can cause batteries to fail quickly rather than giving you a few weeks notice. Batteries will perform best in an environment that is 68-77F. If your room is consistently warmer than that, you may not experience optimal battery performance.

Thanks,

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore