Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:13 AM . Last Modified: 2024-03-18 12:01 AM
I have the SMX3000RMLV2UNC, and when I try to run a self-test it says "Refused", cause "internal fault". The UPS log reports separately "At least one faulty battery exists".
Is the APC refusing a self-test because the battery is bad? Or is the UPS itself also bad? I tried unplugging the unit for a few minutes and disconnecting the battery and nothing changed.
I upgraded the UPS and management card firmware without problems. I know the battery is bad, but is the UPS bad too?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:13 AM . Last Modified: 2024-03-18 12:01 AM
That is the only error/warning on the log screen. I just had thought that the self-test saying internal fault meant my UPS was faulty. Good to hear its okay, thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:13 AM . Last Modified: 2024-03-18 12:01 AM
"At least one battery Fault exists" represent battery is faulty. So u have to order and replace the new battery then the alarm will be reset & try to do the self test.
Do u have any other logs on the Screen? If not, then only battery will be faulty & UPS will be normal Condition.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:13 AM . Last Modified: 2024-03-18 12:01 AM
That is the only error/warning on the log screen. I just had thought that the self-test saying internal fault meant my UPS was faulty. Good to hear its okay, thanks.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.