I have the SMX3000RMLV2UNC, and when I try to run a self-test it says "Refused", cause "internal fault". The UPS log reports separately "At least one faulty battery exists".
Is the APC refusing a self-test because the battery is bad? Or is the UPS itself also bad? I tried unplugging the unit for a few minutes and disconnecting the battery and nothing changed.
I upgraded the UPS and management card firmware without problems. I know the battery is bad, but is the UPS bad too?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:13 AM . Last Modified: 2024-03-18 12:01 AM
That is the only error/warning on the log screen. I just had thought that the self-test saying internal fault meant my UPS was faulty. Good to hear its okay, thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:13 AM . Last Modified: 2024-03-18 12:01 AM
"At least one battery Fault exists" represent battery is faulty. So u have to order and replace the new battery then the alarm will be reset & try to do the self test.
Do u have any other logs on the Screen? If not, then only battery will be faulty & UPS will be normal Condition.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:13 AM . Last Modified: 2024-03-18 12:01 AM
That is the only error/warning on the log screen. I just had thought that the self-test saying internal fault meant my UPS was faulty. Good to hear its okay, thanks.